I think 13 allows the FDC to be connected to the fire line, regardless of what devices are located inside the building. Section 8.17.2.4.4 infers it is acceptable, but you'll still need to install a check valve and the control valve upstream of the FDC connection point (to satisfy 8.17.2.4.1 and 8.16.1.1.4).
Ed Kramer Littleton, CO > -----Original Message----- > From: [EMAIL PROTECTED] [mailto:sprinklerforum- > [EMAIL PROTECTED] On Behalf Of Jamie Seidl > Sent: Thursday, November 13, 2008 1:49 PM > To: [email protected] > Subject: Fire line FDC and Inside controls > > Forum, > I have a situation where the fire department is requiring a post > indicator valve and free standing FDC outside the building. We will > also need a backflow preventer installed inside in the sprinkler control > room. Is it permissible to install the FDC so it ties into the fire > line prior to the backflow control valves, or would we need to install a > separate FDC line into the building? > I know 8.16.1.1.1.3 does not allow a shutoff valve in the line, but it > seems contradictory with Figure A.8.16.1.1 2007 NFPA 13. > Thanks, > Jamie Seidl > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: > [EMAIL PROTECTED] > > To Unsubscribe, send an email to:Sprinklerforum- > [EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)