Anticipated fire load would be key- 30' tall wood structures might exceed the parameters for OH 2. What kind of set material do they plan, height, etc.
Other item would be the amount of shielding from roof spray, smells like EH as in modular home mfg if they're building sets that would have roofs. glc -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Dewayne Martinez Sent: Monday, December 29, 2008 12:05 PM To: [email protected] Subject: Movie studio classification Any ideas on what design density to use for a movie studio? From what I have been told, it will be a 100,000 sq ft building, 50 ft high, broken into 20,000 sq ft sections for different shooting areas. Lets assume that there will be no storage on site and that only the material needed for shooting will be present. Thanks, Dewayne _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)