Looks like the language is identical in the 2008 and 2002 editions. NFPA 70-2002: 110.26(F)(1) (b) Foreign Systems. The area above the dedicated space required by 110.26(F)(1)(a) shall be permitted to contain foreign systems, provided protection is installed to avoid damage to the electrical equipment from condensation, leaks, or breaks in such foreign systems. (c) Sprinkler Protection. Sprinkler protection shall be permitted for the dedicated space where the piping complies with this section. I have taken this section to mean that I can run sprinkler piping in the elec room provided that it is outside the required dedicated space (the width and depth of the panel, cabinet, etc. to a height of 6’ above or to the structural ceiling, whichever is lower) or is above the dedicated space so long as I run a sheet metal gutter under the piping to catch any drips. This language is not intended to prohibit sprinkler protection of the elec room and the sprinkler may discharge into the dedicated space (based on its pattern) so long as the piping to which it is attached is as indicated. Dave
David A. de Vries, P.E., CSP Firetech Engineering Incorporated 2715 Harrison St. Evanston, IL 60201 Tel: 847-733-0944 Fax: 847-866-6255 --- On Mon, 1/5/09, [email protected] <[email protected]> wrote: From: [email protected] <[email protected]> Subject: RE: Electrical Rooms and Archives To: [email protected] Date: Monday, January 5, 2009, 2:30 PM Don't have a 2002 but how does the wording compare to the 2008? Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [email protected] http://www.ch2m.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of David de Vries Sent: Monday, January 05, 2009 3:04 PM To: [email protected] Subject: Electrical Rooms and Archives I usually save Forum postings if I expect to need them in the future. Of course, I thought I knew the rules on dedicated space for electrical equipment well enough that I did not need to save the latest round of discussion on this subject. Now I have the following comment on a submittal: "Provide a note that no HVAC, plumbing or fire sprinkler lines will pass through the electrical rooms. Only what services this room is permitted in this room. 2002 NEC 110.26." I am pretty sure this was discussed in the last month or so and the consensus of the Forum was that there was no such restriction. In one location on the web I went to the AFSA archives, but can't find anything newer than 2004. I may be looking in the wrong place. From the current afsa website, I cannot get the archives (member only?) Can anyone give me a quick tutorial on finding this subject in the archives, please? Dave David A. de Vries, P.E., CSP Firetech Engineering Incorporated 2715 Harrison St. Evanston, IL 60201 Tel: 847-733-0944 Fax: 847-866-6255 _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)