I think the earlier response is the issue.  There is no room to get over to the 
area to be protected, hence
spray the area with the sidewall.  I've wanted to do it on several occasions, 
but just didn't seem right.
There are pendant heads protecting the area behind the sidewall. so the 
alternative is run thru the duct
to get your protection with a pendant.> From: [email protected]> To: 
[email protected]> Date: Mon, 5 Jan 2009 11:47:57 -0700> 
Subject: RE: Sidewall Sprinklers> > Activation is most likely not the issue but 
pattern of discharge. At the wall there is no real need for discharge in more 
than one direction as opposed to a pendent or upright in the middle of a room 
where you're seeking a 360 degree field of discharge.> > Same deal for the 
sidewall under the garage door. Beyond the door the ceiling sprinks do their 
job, SW is only concerned with one direction, the space below the door.> > > 
Craig L. Prahl, CET > Fire Protection Specialist> Mechanical Department> 
CH2MHILL> Lockwood Greene> 1500 International Drive> PO Box 491, Spartanburg, 
SC 29304-0491> Direct - 864.599.4102> Fax - 864.599.8439> [email protected]> 
http://www.ch2m.com > > > -----Original Message-----> From: 
[email protected] 
[mailto:[email protected]] On Behalf Of George Church> 
Sent: Monday, January 05, 2009 1:44 PM> To: [email protected]> 
Subject: RE: Sidewall Sprinklers> > I'm not a PE nor do I play one on TV. But 
I've seen James' fire videos, so I'm ahead of most plumbing designers:)> > 
Caveats aside, I think activation depends on heat banking down from the 
ceiling, and in order to get a head to throw 24' it has to go off- and that's a 
long way for heat to go without a backdrop to stop heat from continuing to the 
next SSP below a flat ceiling. The "wall" or soffit behind the SW will stop 
that heat from continuing past it and turn it toward the thermal element. Heat 
Creep?> > I've never been a fan of protecting a 48' wide area by ECHSW on 
opposing walls. Wouldn't think there'd be much life safety offered. > > glc> > 
-----Original Message-----> From: [email protected]> 
[mailto:[email protected]] On Behalf Of A.P.Silva> Sent: 
Monday, January 05, 2009 1:32 PM> To: [email protected]> 
Subject: RE: Sidewall Sprinklers> > I agree, the codes do not permit 
installation of sidewalls without a backwall/soffit/beam in any other 
situation. However, this is something I have often wondered myself. Granted, 
all closed sprinklers actuated by thermal elements require to be in proximity 
to a ceiling. The thermal elements in sidewalls are the same as pendents and 
uprights. So why would only sidewall also require a backwall? Is the acuation 
of sidewalls different from pendents and uprights? I think the originator of 
this post is asking a valid question.> > Tony > > -----Original Message-----> 
From: [email protected]> 
[mailto:[email protected]] On Behalf Of Roland Huggins> 
Sent: January 5, 2009 8:55 AM> To: [email protected]> Subject: 
Re: Sidewall Sprinklers> > The only exception to not having a wall, soffit, or 
beam behind them is when installed UNDER roll-up doors ( as allowed by 8.4.2 
(3)> > Roland> > On Dec 31, 2008, at 11:37 AM, Dale Wingard wrote:> > > Duane,> 
>> > NFPA 13(2007) 8.7.4.1.2 addresses the location of vertical and > > 
horizontal sidewalls in relation to the wall that they are projected > > from.> 
>> > Sidewall sprinklers cannot be positioned in the center of a room as a > > 
pendant.> >> >> > Dale F. Wingard, SET> > Design Manager> > Triple "A" Fire 
Protection, Inc.> > 251.649.2034> > [email protected]> >> >> > -----Original 
Message-----> > From: [email protected]> > 
[mailto:[email protected]] On Behalf Of > > Johnson, 
Duane (NIH/OD/ORS) [C]> > Sent: Wednesday, December 31, 2008 11:34 AM> > To: 
[email protected]> > Subject: Sidewall Sprinklers> >> >> > Can a 
horizontal sidewall sprinkler be installed in the center of a > > room (flat, 
smooth clg) provided sprinkler coverage is added behind > > the sidewall? In 
other words, not installed near a wall or soffit.> >> > In reality a sidewall 
installed 4" to 6" below the ceiling (away from > > a> > wall/soffit) should 
activate in similar fashion as exposed pendents > > and uprights (1" - 12" 
below clg). If code permits "exposed"> > sidewalls to be installed below roll 
up doors without soffits, can't > > an "exposed"> > sidewall be installed 
elsewhere?> >> > Is there anything in the listing of a sidewall that requires 
the > > sprinkler be installed on a wall or soffit? Are there any ROP/ROC > > 
responses from the committee that would help answer the question?> >> > 
Thoughts?> >> > Duane Johnson, PE> > Program Manager> > Division of the Fire 
Marshal (Support Contractor) Office of Research > > Services National 
Institutes of Health> > 301-496-0487> > 
_______________________________________________> > Sprinklerforum mailing list> 
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> > For 
Technical Assistance, send an email to:> > [email protected]> >> > 
To Unsubscribe, send an email> > to:[email protected]> > 
(Put the word unsubscribe in the subject field) > > 
_______________________________________________> > Sprinklerforum mailing list> 
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> > For 
Technical Assistance, send an email to: > > [email protected]> >> > 
To Unsubscribe, send an email> > to:[email protected]> > 
(Put the word unsubscribe in the subject field)> >> > 
_______________________________________________> Sprinklerforum mailing list> 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> For Technical 
Assistance, send an email to: [email protected]> > To Unsubscribe, 
send an email to:[email protected]> (Put the word 
unsubscribe in the subject field)> > 
_______________________________________________> Sprinklerforum mailing list> 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> For Technical 
Assistance, send an email to: [email protected]> > To Unsubscribe, 
send an email to:[email protected]> (Put the word 
unsubscribe in the subject field)> > 
_______________________________________________> Sprinklerforum mailing list> 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> For Technical 
Assistance, send an email to: [email protected]> > To Unsubscribe, 
send an email to:[email protected]> (Put the word 
unsubscribe in the subject field)> 
_______________________________________________> Sprinklerforum mailing list> 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> For Technical 
Assistance, send an email to: [email protected]> > To Unsubscribe, 
send an email to:[email protected]> (Put the word 
unsubscribe in the subject field)_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to