Hey just get an AHJ to sign off on the concept, then it's all good!   ;) 

Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Thom McMahon
Sent: Monday, January 05, 2009 4:45 PM
To: [email protected]
Subject: RE: Sidewall Sprinklers

All Dandy idea's. Now all you need to do is show that there is enough need for 
this to have UL and FM develop a standard test for this installation, then 
convince the MFG's that the demand for this installation is great enough for 
them to spend 100's of thousands of $ to get the testing and listing done.(If 
each of them tried to list just 3 HSW heads, that would be over a million $.

Takes a lot of HSW in "Space" installations to recover that kind of investment. 
Also I heard something about an economic down turn in the economy, where money 
is hard to get. That could just slow things down for several years.


Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Johnson, Duane 
(NIH/OD/ORS) [C]
Sent: Monday, January 05, 2009 2:05 PM
To: [email protected]
Subject: RE: Sidewall Sprinklers

Looking at 155°F EC pendents and uprights, 20x20 are standard response and
18x18 (or less) are quick response.  In other words, the sprinkler is either 9' 
away or 10' away from the fire.

This leads one to believe that it would be possible to have an exposed HSW 
listed for a 10' throw for at least standard response, maybe quick response.
Note, that if a 'recessed' or even 'concealed' pendent can get a listing at 9' 
or 10' away from the fire, you would think an exposed sidewall 4'-6"
below the ceiling could receive a listing.  Especially since 4"-6" below the 
ceiling is more ideal for a quick activation time than a recessed pendent.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor) Office of Research Services 
National Institutes of Health
301-496-0487


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to