thank you again for your suggestions.

the water supply comes from various tanks and reservoirs.
these tanks and reservoirs provide 4 hour supply at hydrant flow rates.
the water is delivered by a loop around the building.
we need to boost pressure to get automatic standpipes.
I am hoping the fire department will accept manual, wet standpipes.

scot deal
excelsior fire engineering


Is the water supply part of a larger grid system or is the loop
supplied from a single source, and for this project only? What I'm getting
at, is it may be preferable to have the fire pump supply the site main
(Loop) rather than the individual risers.