I would never suggest a fire pump on each run-in.  Hopefully the site has been 
thought out and the loop supplying the new building can be boosted through the 
pump(s).


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Thom McMahon
Sent: Monday, January 26, 2009 10:55 AM
To: [email protected]
Subject: RE: when is redundancy a good thing... 1 vs 2 water lead-ins to 
abuilding

I agree with the assessment that a single run-in to the building is not good 
design. I question multi-fire pumps? You say the building has a looped water 
supply? Is the water supply part of a larger grid system or is the loop 
supplied from a single source, and for this project only? What I'm getting at, 
is it may be preferable to have the fire pump supply the site main
(Loop) rather than the individual risers.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926




You have 820,000 sq. ft. and only one run-in?  Say it isn't so.


You need to break up these systems and provide for multiple run-ins.


If the fire pump is necessary to make the systems work then I see no problem 
with submitting a primary and backup fire pump for this size and occupancy of a 
building.  I mean almost a million sq. ft and 10,000 people?  What's the value 
of one life versus a fire pump, for the legal award for one loss you could buy 
quite a few pumps.


Craig L. Prahl, CET   

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to