I have done several prisons and have always counted any evidence room (either paper or object storage) as OHII. The fire Marshalls here have never sent it back to be changed.
Karen Purvis Designer Facility Systems Consultants 714 S Gay St Knoxville, TN 37902 ph.865-246-0164 fax 865-246-1084 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Chris Russel Sent: Wednesday, February 04, 2009 4:26 PM To: [email protected] Subject: Evedence Room Hello Does anyone have any experience with coverage of a police evidence room? Our fire marshal says Light Hazard won't cut it. I agree but I don't think anything more than OH II is necessary; however I was wondering if anyone has experience with this. If so, what hazard was it designed to? Thanks, Chris Russell t. 360.734.4940 f. 360.647.9540 securitysolutionsnw.com _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)