Could some of the more urban Forumites tell us what hazard a seized crack
lab is, when placed in an evidence room?

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Wednesday, February 04, 2009 4:59 PM
To: [email protected]
Subject: Re: Evedence Room

Chris,

You need to look at this just like any other storage occupancy. It 
can also depend on where you are. An Evidence Room in Los Angeles 
could be very different than one in East Wazoo. Is this for current 
cases or archival storage? Shelves? Racks? How high? If your storage 
is less than 12 ft, it would fall into Miscellaneous Storage. The 
commodity class could be all over the lot, but Class III or IV could 
be appropriate. Chances are, probably not a lot of foamed plastic.


At 04:26 PM 2/4/2009, you wrote:
>Hello
>
>Does anyone have any experience with coverage of a police evidence room?
Our
>fire marshal says Light Hazard won't cut it. I agree but I don't think
>anything more than OH II is necessary; however I was wondering if anyone
has
>experience with this. If so, what hazard was it designed to?
>
>
>
>Thanks,
>
>
>
>Chris Russell
>
>
>
>t. 360.734.4940
>f. 360.647.9540
>
>securitysolutionsnw.com
>
>
>
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to