Chris,

You need to look at this just like any other storage occupancy. It can also depend on where you are. An Evidence Room in Los Angeles could be very different than one in East Wazoo. Is this for current cases or archival storage? Shelves? Racks? How high? If your storage is less than 12 ft, it would fall into Miscellaneous Storage. The commodity class could be all over the lot, but Class III or IV could be appropriate. Chances are, probably not a lot of foamed plastic.