Yes but as I said you only get there exclusively when you exceed the storage
heights in 910.3 or the S occupancy is less than 50,000 sq.ft.  If you are
over 50,000 sq.ft. and under 40' (30' for high hazard) of storage wouldn't
910.3 still apply?  The theoretical purpose of ch. 23 is to deal with the
specific hazard of HPS even when only 500 sq.ft.  910 is to deal with the
specific hazard of buildings over 50,000 sq.ft. of certain occupancies.  I
believe the intention of is to except all smoke control for ESFR, but I
don't see that in the black and white and am normally hesitate to assume the
intention of the committees. I try to literally read what is there for good
and for bad.      

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Sunday, February 15, 2009 7:54 AM
To: [email protected]
Subject: RE: ESFR Systems

Chris,

2006 IFC Table 2306.2 contains exceptions for venting and draft curtains
in ESFR facilities.  Is this relevant to your point?

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell

-------- Original Message --------
Subject: RE: ESFR Systems
From: "Chris Cahill" <[email protected]>
Date: Fri, February 13, 2009 9:05 am
To: <[email protected]>

Unless I'm missing something I don't see where ESFR gets one out of
smoke
and heat venting in F-1 or S-1 occupancies when over 50,000 sq.ft. I'm
looking in IBC 910 or IFC 910.

I see draft curtains are traded of ESFR 910.3.4.

I'd go even further in that the chart 910.3 doesn't recognize the ESFR
exception in the IFC for HPS. The footnote says when in excess of the
chart
shall be in accordance with IFC ch. 23.

So for 18' of storage and over 50,000 sq.ft. as I see it still requires
smoke and heat venting even with ESFR.

And as far as putting in ESFR in non-HPS or spec buildings it's done all
the
time at various heights. I agree it shouldn't. I really love the ones
(like all) where they don't allow in the calc's for an extra head or two
for
future obstructions.

Perhaps if one is quick we can get a prohibition of ESFR in shell spaces
in
place for like 2022. That would be the 2016 edition plus the time it
takes
for anyone to actually adopt.

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.

763-658-4483
763-658-4921 fax

Email: [email protected]

Mail: P.O. Box 69
 Waverly, MN 55390

Location: 4439 Hwy 12 SW
 Waverly, MN 55390
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Mark
Sornsin
Sent: Thursday, February 12, 2009 3:47 PM
To: '[email protected]'
Subject: RE: ESFR Systems

That's correct - for F-1 occupancies with more than 50,000 sq.ft. of
area.
But ESFR is the wrong technology for that type of occupancy (outside of
the
high-piled storage areas anyway). Unfortunately, that fact is not made
clear
in the codes (I'm referencing 2006 IFC).

Mark

-----Original Message-----
From: [email protected] [mailto:[email protected]]
Sent: Thursday, February 12, 2009 3:40 PM
To: [email protected]
Cc: Mark Sornsin
Subject: RE: ESFR Systems

There may be a building code issue involved,whereas by using an "ESFR"
sprinkler
system, any need for roof ventilation(fans,draft curtains,etc.) may be
eliminated.I encountered this on a similar manufacturing facility.


Lamar Vaughn,SET
Vaughn & Company
McDonough,GA

--- Mark Sornsin <[email protected]> wrote:
> The owner sounds uninformed about ESFR technology. Since there will be no
high-piled storage (no commodity), there should be no incentive to use
ESFR
and deal with the flows and obstruction concerns that come with them.
Why
have a 54 Ft. building without high-piled storage? Sounds like a
building
filled with process equipment or the like - certainly a better place for
the
density/area approach (or comparable special design).
>
> Mark A. Sornsin, PE
> Fire Protection Engineer
> Ulteig Engineers, Inc.
> Fargo, ND
> Direct: 701. 280.8591
> [email protected]
>
>

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to