The owner sounds uninformed about ESFR technology. Since there will be no high-piled storage (no commodity), there should be no incentive to use ESFR and deal with the flows and obstruction concerns that come with them. Why have a 54 Ft. building without high-piled storage? Sounds like a building filled with process equipment or the like - certainly a better place for the density/area approach (or comparable special design).
Mark A. Sornsin, PE Fire Protection Engineer Ulteig Engineers, Inc. Fargo, ND Direct: 701. 280.8591 [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Steve Leyton Sent: Thursday, February 12, 2009 2:59 PM To: [email protected] Subject: RE: ESFR Systems And also maximum distance from the commodity? Steve Leyton Protection Design & Consulting San Diego, CA -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Travis Mack, SET Sent: Thursday, February 12, 2009 11:57 AM To: [email protected] Subject: RE: ESFR Systems I believe 45' is the highest they are listed to be used. Check the data sheets to be sure. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Dennis Browning Sent: Thursday, February 12, 2009 12:40 PM To: [email protected] Subject: ESFR Systems I have a 54' tall building that the owner is suggesting ESFR system design. Is there a limit on building height for that type system. This building will NOT have rack or high piled storage. Dennis Browning Browning Fire Medford, Oregon _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)