There may  be a building code issue involved,whereas by using an "ESFR" 
sprinkler
system, any need for roof ventilation(fans,draft curtains,etc.) may be 
eliminated.I encountered this on a similar manufacturing facility.


Lamar Vaughn,SET
Vaughn & Company
McDonough,GA
 
--- Mark Sornsin <[email protected]> wrote: 
> The owner sounds uninformed about ESFR technology. Since there will be no 
> high-piled storage (no commodity), there should be no incentive to use ESFR 
> and deal with the flows and obstruction concerns that come with them.  Why 
> have a 54 Ft. building without high-piled storage?  Sounds like a building 
> filled with process equipment or the like - certainly a better place for the 
> density/area approach (or comparable special design).
> 
> Mark A. Sornsin, PE
> Fire Protection Engineer
> Ulteig Engineers, Inc.
> Fargo, ND
> Direct:    701. 280.8591
> [email protected]
> 
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Steve Leyton
> Sent: Thursday, February 12, 2009 2:59 PM
> To: [email protected]
> Subject: RE: ESFR Systems
> 
> And also maximum distance from the commodity?
> 
> Steve Leyton
> Protection Design & Consulting
> San Diego, CA
> 
> 
> 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Travis
> Mack, SET
> Sent: Thursday, February 12, 2009 11:57 AM
> To: [email protected]
> Subject: RE: ESFR Systems
> 
> I believe 45' is the highest they are listed to be used.  Check the data
> sheets to be sure.
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Dennis
> Browning
> Sent: Thursday, February 12, 2009 12:40 PM
> To: [email protected]
> Subject: ESFR Systems
> 
> I have a 54' tall building that the owner is suggesting ESFR system
> design.
> Is there a limit on building height for that type system. This building
> will
> NOT have rack or high piled storage.
> 
> Dennis Browning
> Browning Fire
> Medford, Oregon
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to