I read about a case involving circumstances very similar to those you
describe.  According to the article (from a major insurer of fire sprinkler
contractors) a fire occurred under the unprotected canopy and flashed over
into the store, resulting in a significant loss.  Interestingly, the
contractor who performed inspections there wound up taking the hit since
he'd not noted the unprotected area on inspection reports, but HAD noted
other, perhaps lesser, installation code observations in other areas of the
shopping center.  

That doesn't specifically answer your question, but it should provide some
compelling evidence to support fully sprinklering the building.    

Paul S Johnson
Bardane, Inc. Visioning a competitive workforce
(407) 401-7154 - Office
(407) 399-5081 - Mobile 
[email protected]
www.bardane.net 
 
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Monday, February 23, 2009 3:54 PM
To: [email protected]
Subject: Exterior canopies at grocery stores: do they need sprinklered?


I have a question: Your typical grocery store with exterior canopy,
noncombustible or limited-combustible construction. Code is NFPA 13 2007
edition.

8.15.7.2 permits omission of sprinklers if it is non-combustible. In
commentary, the book gives a drive up bank windows, and hotel canopies as
examples where they would likely be ommitted. 

8.15.7.5 says sprinklers are required over areas where combustibles "are
stored and handled."

I see grocery stores with and without sprinklers in the outside canopies.

Is placing a pallet of Christmas trees (during Christmas) outside or a
pallett of BBQ Briquets during summer ouside constitute "Storage," or
"handling of combustibles?"

In your opinion, do these grocery stores meet the criteria for omission?

Forest Wilson
Cherokee Fire
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to