Thinking they missed a cut when cutting and pasting from the last letter.  

And even if it's true in their opinion, changing the remote area is not a
consideration in hazard analysis like this.  In-other-words it appears they
are agreeing with light hazard but want 1500 sq.ft.  If they are concerned
with higher than normal fire potential the correct comment would be to
change the hazard classification.  Yes then there are cases to further
change the RA but that's not my first move.  

And I don't think they get to make evaluations like that on a peer review.
If they wrote the spec fine you have a problem.  Here it's strictly per 13.
I think both prisons and residential are rather well covered it the
standard.  

Ask where you were employed to practice engineering in the first place.  See
now if you said you engineered the system I bet they'd rightfully call you
on it.  (assuming you don't have engineers)  Good or bad your job I'd bet
has nothing to do with engineering.  

A single company does not get to set good engineering practices.  They are
only developed through industry standards.  An engineering company might
have engineering opinions but unless they have some ASTM, NFPA, SFPE
document I've not heard of talking about the engineering practice in this
case it ain't a good or bad practice.

I'd love them to articulate what is normal for prisons or residential in the
first place. Unless they can quantify normal they can't judge higher. 

Here's another twist they might be thinking of.  The frequency of fire they
may be concerned with.  They say "potential for a fire" not "fire potential"
which could be interpreted as the frequency vs. the size.  Now I doubt
frequency is a concern in prison.  And NFPA 13 and all its good and bad have
really nothing to do with frequency or risk of a fire starting IT ASSUMES A
FIRE HAS STARTED.

Hey I'll peer review it for you but I think good engineering practice is for
a full 2500 sq.ft. hahahahahaha 

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Fletcher, Ron
Sent: Wednesday, February 25, 2009 5:03 PM
To: [email protected]
Subject: PE Peer Review

I would like the take from the PE's on forum on how to deal with a plan
review comment from an unnamed engineering firm (RJA).

"Due to the higher than normal potential for a fire in the occupant
sleeping and common areas, the reduction in fire are (remote area) for
quick response sprinkler in accordance with NFPA #13 Figure 11.2.3.2.3.1
is not a good engineering practice. Please revise the hydraulic
calculation to account for at least the minimum 1500 square foot design
area as specified by NFPA #13."

The hazard is a dormitory at a minimum security prison.

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to