Yeah... I was reading the data sheets this morning. LOVED the paragraph
about the small plastic containers of oil.. Something like. "System will
either work if early on small fire, or will fail altogether" LOL. Even
though it is IIIB, the arrangement and Volume is scary. Not to mention the
mix.

R/
Matt

Matthew J. Willis
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-387-1163 Facsimile
[email protected]
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Rodney Hamm
Sent: Thursday, March 05, 2009 3:59 PM
To: [email protected]
Subject: Re: Rack Storage of Motor Oil

Matt,



You have some VERY complicated and high hazard issues at this warehouse.



I would suggest finding someone well versed in fire protection schemes
involving flammable/combustible liquids AND you should take a long hard look
at FM Global Data Sheet 7-29. The non-confidential version of the data sheet
is free on the internet
(http://www.fmglobal.com/FMGlobalRegistration/default.aspx?action=new).



Good luck and be careful (from a design & liability standpoint)..a fire
incident involving the storage arrangements you described could be severe!



Rodney K. Hamm, P.E.
President/Owner
Falcon Fire Protection
Office  (478) 953-1677

Cell  (478) 396-6988



Date: Thu, 5 Mar 2009 10:53:54 -0600

From: "Matthew J. Willis" <[email protected]>

Subject: Rack Storage of Motor Oil

To: <[email protected]>

Message-ID: <f2161fdd99ac42358548955d589a1...@matt>

Content-Type: text/plain;     charset="iso-8859-1"



I am looking to do an evaluation of a warehouse (originally manufacturing

.20/1500) that has now been bought by an oil distributor. When I walked

around looking, all kinds of red flags went off. I am now concerned that we

cannot get there from here. Gut says this is outside of sprinkler

protection. So I want to be sure before I say we cannot help you. Bulk of

product is standard motor oil in non-relieving drums (55gal), stored on

racks, mostly 3 high. Also contained in same warehouse throughout is solid

pile storage to around 12_ of cases of 1qt (plastic) containers that you

would purchase from your favorite reseller. Mixed in are gallon containers

of anti-freeze stored solid pile as the 1qt containers of oil. Not to

mention the moderate placement of Varsol and starter fluid here and there.

This space appears to be just under 80,000 Sq Ft. Of course there is no

containment or other controlling measurers built into floor or racks. The 1,

1, 1< branch lines looked awful lonely at the roof..







Thanks,



Matt







Matthew J. Willis



Norred Fire Systems L.L.C.



318-387-1134 Voice



318-387-1163 Facsimile



[email protected]

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to