Matt,
I would first find out what codes the local jurisdiction has adopted.
Then ask for MSDS and quantities. Figure out exactly what type of fluids
he has stored. Flammable, combustibles, corrosives, etc...If they use
the international fire code start there. You will find certain chapters
on what material is being stored.dispensed etc..They are only allowed so
much storage based on control areas. Then only allowed so many control
areas on a single floor. Once you have that information see if the
building is zoned for that type of storage. Then a PE can tell you what
type of density you need for that storage. I hope that helps. Tom 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Rodney
Hamm
Sent: Thursday, March 05, 2009 3:59 PM
To: [email protected]
Subject: Re: Rack Storage of Motor Oil

Matt,

 

You have some VERY complicated and high hazard issues at this warehouse.

 

I would suggest finding someone well versed in fire protection schemes
involving flammable/combustible liquids AND you should take a long hard
look
at FM Global Data Sheet 7-29. The non-confidential version of the data
sheet
is free on the internet
(http://www.fmglobal.com/FMGlobalRegistration/default.aspx?action=new).

 

Good luck and be careful (from a design & liability standpoint)..a fire
incident involving the storage arrangements you described could be
severe!

 

Rodney K. Hamm, P.E.
President/Owner
Falcon Fire Protection
Office  (478) 953-1677

Cell  (478) 396-6988

 

Date: Thu, 5 Mar 2009 10:53:54 -0600

From: "Matthew J. Willis" <[email protected]>

Subject: Rack Storage of Motor Oil

To: <[email protected]>

Message-ID: <f2161fdd99ac42358548955d589a1...@matt>

Content-Type: text/plain;     charset="iso-8859-1"

 

I am looking to do an evaluation of a warehouse (originally
manufacturing

.20/1500) that has now been bought by an oil distributor. When I walked

around looking, all kinds of red flags went off. I am now concerned that
we

cannot get there from here. Gut says this is outside of sprinkler

protection. So I want to be sure before I say we cannot help you. Bulk
of

product is standard motor oil in non-relieving drums (55gal), stored on

racks, mostly 3 high. Also contained in same warehouse throughout is
solid

pile storage to around 12_ of cases of 1qt (plastic) containers that you

would purchase from your favorite reseller. Mixed in are gallon
containers

of anti-freeze stored solid pile as the 1qt containers of oil. Not to

mention the moderate placement of Varsol and starter fluid here and
there.

This space appears to be just under 80,000 Sq Ft. Of course there is no

containment or other controlling measurers built into floor or racks.
The 1,

1, 1< branch lines looked awful lonely at the roof..

 

 

 

Thanks,

 

Matt

 

 

 

Matthew J. Willis

 

Norred Fire Systems L.L.C.

 

318-387-1134 Voice

 

318-387-1163 Facsimile

 

[email protected]

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to