Thanks guys.

This one was a borderline if I would do it or get a PE involved. The
existing supply is 8" with pretty good pressure. The sprinklers are spaced
around 110. 120 is allowed for Class IIIB. Branch lines will have to go,
along with 1/2" sprinklers. There are 5 mains, not sure why, but it is old
screwed schedule system, with a couple 6" Main Mains (not from chapter 3). I
will pass on this one. The class and rack configurations were not so much a
worry as the smaller containers piled everywhere. Kinda like seeing a Ford
engine in a Chevy, just doesn't look right. Besides I think this will
qualify for state requirement of professional. 

R/
Matt

Matthew J. Willis
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-387-1163 Facsimile
[email protected]

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Thursday, March 05, 2009 5:05 PM
To: [email protected]
Subject: RE: Rack Storage of Motor Oil

As Craig said, this could be worse (200+ gallon totes of this stuff
and worse.) They really need to get an FPE involved who has worked
with this type of occupancy to figure out storage arrangements and
come up with criteria. Assume that the existing piping will have to
be ripped out and replaced with new. Hopefully the underground is at
least 6". Also get a new flow test. That could be critical on how you
proceed. Good Luck



At 05:41 PM 3/5/2009, you wrote:
>Dude, what you've got there is a piece of cake compared to some of
>the stuff we deal with on a regular basis.  I'd love to have
>something as simple as that now and then.  <sigh>
>
>It's really not as bad as you think, but I realize if it's not a
>regular menu item it can be kind of daunting.
>
>There are just a lot of questions that need answered.
>
>NFPA 30 has this addressed.  IIIB's as far as combustibles are at
>the bottom of the list, least hazardous, quantities allowed are
>rather generous per the IBC.  Also and depending on arrangements and
>quantities you will need to define this space per the IFC/IBC.
>
>Regardless, you can pretty much tell the owner that the system he
>has now ain't gonna fly with this new arrangement.  Going from a
>Factory to Storage occupancy rarely transitions easily.
>
>If you decide to move forward with it you need to employ someone
>with good code familiarization and special hazards experience.  This
>is no simple "apply NFPA 13 and all local,state,federal and
>inter-galactic codes" kind of job.
>
>Like I said, there are a lot of issues that need to be uncovered and
>researched but it's not that bad.
>
>Craig L. Prahl, CET
>Fire Protection Specialist
>Mechanical Department
>CH2MHILL
>Lockwood Greene
>1500 International Drive
>PO Box 491, Spartanburg, SC  29304-0491
>Direct - 864.599.4102
>Fax - 864.599.8439
>[email protected]
>http://www.ch2m.com
>

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to