Thermal Expansion & Water Hammer

One of the consequences of installing a backflow prevention assembly on any
water system is the system becoming a closed system. A closed system is a
system, which is not open to the atmosphere. A pressurized tank would be a
closed system, since there is no means for the pressure to escape.
A water user's system may be considered an open system if there is no
backflow protection. Water flows from the water supplier into the water
user's premises through the water meter. Should something cause the pressure
on the water user's property to increase, water can freely flow back out
into the water distribution system.
What can cause the water user's system to increase in pressure?

A common phenomenon, which increases pressure, is thermal expansion. Thermal
expansion occurs when water in the pipes heats up. This may be due to
environmental conditions such as a hot room, or it may be caused by a piece
of water-using equipment that is generating heat. Regardless of what causes
the water to heat up, when it does it expands and requires more volume. This
is no problem in an open system, the water flows back through the meter into
the distribution system. However, when the system is a closed system, which
occurs when a double check valve assembly or a reduced pressure principle
assembly is installed; the water doesn't have anywhere to go. In these
conditions the pressure can increase dramatically.

Another phenomenon occurring in hydraulic systems is a water hammer. A water
hammer occurs when the flow of water through a pipe is stopped quickly. This
may occur because of a solenoid valve, or even a quarter-turn ball valve
being closed too quickly. The flowing water is stopped when it hits the
closed valve, but a shock wave is sent back in the opposite direction.
Again, this wave would dissipate if the system was an open system. However,
in a system, which is closed, because of a backflow preventer, the shock
wave will hit the downstream check valve of the backflow preventer and the
wave will move back throughout the system. This may increase the pressure
throughout the system up to several times the normal water pressure. This is
enough to cause significant damage in equipment and water fixtures. In a
mathematical model, water flowing at 15 feet per second through pipe
generated an increase in pressure of over 900 pounds per square inch (psi),
when a downstream valve was closed instantaneously.
What can be done to prevent damage in a system subjected to either water
hammer or thermal expansion?

Expansion Tank
Under the thermal expansion situation described above, the system could be
protected by the installation of an expansion tank. An expansion tank is
attached to the water system and may be pressurized with air on one side of
a diaphragm within the tank. When the water pressure increases due to
thermal expansion, the tank begins tfill with water pressurizing the air on
the other side of the diaphragm. Water is not compressible, so when the
water begins to expand due to heat, it needs to go somewhere. Air on the
other hand is compressible. So, the expanded water goes into one side of the
tank compressing the air on the other side. This prevents any part of the
system from giving way to the expanding water.

Although an expansion tank may help solve a thermal expansion problem, water
hammer may be so powerful that an expansion tank won't take care of the
problem. A water hammer arrester may be installed to reduce the effects of
the water hammer. In some cases some re-engineering of the system may be
necessary. For example, at the industrial complex, the solenoid valve was
adjusted to close very slowly. So, instead of closing nearly
instantaneously, the closure was very slow and thus, the water hammer was
eliminated.

Courtesy of the USC School of Engineering
Foundation for Cross-Connection Control and Hydraulic Research
http://www.wvdhhr.org/phs/water/Thermal_Expansion.pdf

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Rodney Hamm
Sent: Wednesday, March 18, 2009 9:23 PM
To: [email protected]
Subject: Excessive system pressure

I find it VERY interesting that it has been over a week since I
suggested/challenged the forum participants to a simple experiment and there
has been exactly ZERO responses to report any conclusions/findings. 

 

I am wondering if anyone actually tried the experiment referenced
below....if so, I wonder why has there been no response through the forum?
Could it be that some have spent the 4-5 minutes and have decided against
posting a response because the experiment does not support their theory?
Could it possibly be that the various forum participants who believe water
compression is the root cause of high system pressures are to "old school"
and "close minded" (to use a phrase that was used to describe me..heh heh
heh..really funny if you knew me at all) to consider a simple experiment
that might in any way challenge their way of thinking? Or could it possibly
be that water and air act differently to temperature changes in Georgia than
any other place in the world? 

 

I am having a little too much fun with this email.

 

On a more serious note, I was at another plant yesterday which has the same
exact problem. This is really why I am writing this email. Warehouse with 1
gridded system and 7 tree fed systems. The problem only exists for the
gridded system; the remaining 7 systems had nominal pressure differences
(0-10 psi difference) between the top & bottom gauges. On the gridded
system, the public pressure upstream of the alarm check valve was fairly
steady all afternoon at ~60 psi. At 1:50 PM, the system pressure downstream
of the alarm check valve was 190 psi. I described the problem to the plant
engineer and he wanted me to explain the problem to the plant manager. The
three of us returned to the riser at 2:10 PM and the system pressure
downstream of the alarm check valve was already up to 205 psi. We have not
even entered our really hot days of summer yet! Riser nipples on the near
main and the far main and the ITC for the system was attached to the bottom
of the far main (in other words, the auxiliary or low point drain was
converted into an ITC by installing the base of a sprinkler head at the end
of the pipe and then someone placed an ITC sign on the valve). This system
was installed prior to the NFPA requirement of a 175 psi PRV for all gridded
systems. I have recommended the provision of a 175 psi PRV, installing air
bleed off valves and removing a significant amount of the trapped air from
the system. The ITC piping "SHOULD" be arranged to flow water through the
highest point of the system whenever possible, but some people just don't
give a damn!

 

 

Rodney K. Hamm, P.E.
President/Owner
Falcon Fire Protection
Office  (478) 953-1677

Cell  (478) 396-6988

 

Date: Wed, 11 Mar 2009 15:47:19 -0400

From: "Rodney Hamm" <[email protected]>

Subject: RE: Test/Drain at the Riser

To: <[email protected]>

Message-ID: <[email protected]>

Content-Type: text/plain;     charset="us-ascii"

 

I challenge you to try my suggested experiment! Even if you do not want to
try it..try it with a preconceived notion that I am completely wrong.

 

Take a completely 100% full glass of cold water (plastic would be best) pull
some saran wrap over the top very tight and add a rubber band really tight
to make sure no air leaks out. Make sure there are no air bubbles on top.
Put the full glass of water in the microwave on HIGH for 2 minutes. No
pressure builds up inside the glass because water is not compressible and
does not expand. Pressure will eventually build if you let the water start
to boil. THEN do the same exact thing with a glass half full of cold water.
Using saran wrap and a tight rubber band, you will see the pressure
increases dramatically and eventually will burst the saran wrap after the
balloon effect!

 

The results will be so obvious you will see my point. The plastic film on
top allows you to see the dramatic difference in pressure increase (100%
water vs. 50% air). My experiment is actually a closed system. I will agree
that the volume is allowed to increase, but the only force which allows the
plastic film to balloon is due to the increased pressure in the closed
container. If the same percentage of water/air was in a sprinkler pipe, the
increased pressure caused by the temperature increase would cause the system
pressure to increase dramatically due to the fact that there is no change in
volume (until a leak or system rupture occurs). Of course, the best test
environment would be to use a sprinkler system in an oven with a calibrated
pressure gauge, but most of our forum readers would never take this much
time and effort. The experiment I suggested is VERY convincing if you are
willing to spend 5 minutes of your time to try.

 

Air is compressible and water is not compressible. Temperature increases or
decreases do not affect the pressure of a section of pipe filled with 100%
water until the water begins to boil. Temperature increases will cause the
pressure to increase if the same section of pipe is filled with air or has a
significant percentage of air along with some water. Temperature decreases
will cause the pressure to decrease if the same section of pipe is filled
with air or has a significant percentage of air along with some water.

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to