The building owner wants to connect the discharge piping from the pump
relief valve to the pump suction pipe, just upstream of the suction valve.
The water supply to the pump is a water storage tank. Anyone seen this
arrangement? Is it acceptable? 

NFPA 20, 2007 section 5.18.7 mentions "Discharge to Source of Supply". Is
this to the tank or can it be also to the suction pipe? Both 5.18.7 and
A5.18.7, seems to have a concern regarding the size of the relief valve and
discharge piping, but does not provide much guidance (in my opinion). Anyone
care to expand on this concern?

The fire pump is rated 1000 gpm @ 105 psi. The source as mentioned
previously, are gravity tanks. The relief valve is 4" and discharge pipe is
8" corresponding to Table 5.25. The discharge piping from the relief valve
to connection at pump suction pipe has one elbow. At the connection to the
pump suction there is a tee. Is the tee to be counted and the sizing be
increased as per 5.18.6.2 ?

Any pump experts?

Tony    