How about a more basic question.  Why do you even have a relief  
valve?  With a rating of only 105 psi exceeding 175 psi with a tank  
feed requires a tall tank.

Roland

On Mar 19, 2009, at 11:23 PM, A.P.Silva wrote:

>
> The building owner wants to connect the discharge piping from the pump
> relief valve to the pump suction pipe, just upstream of the suction  
> valve.
> The water supply to the pump is a water storage tank. Anyone seen this
> arrangement? Is it acceptable?
>
> NFPA 20, 2007 section 5.18.7 mentions "Discharge to Source of  
> Supply". Is
> this to the tank or can it be also to the suction pipe? Both 5.18.7  
> and
> A5.18.7, seems to have a concern regarding the size of the relief  
> valve and
> discharge piping, but does not provide much guidance (in my  
> opinion). Anyone
> care to expand on this concern?
>
> The fire pump is rated 1000 gpm @ 105 psi. The source as mentioned
> previously, are gravity tanks. The relief valve is 4" and discharge  
> pipe is
> 8" corresponding to Table 5.25. The discharge piping from the relief  
> valve
> to connection at pump suction pipe has one elbow. At the connection  
> to the
> pump suction there is a tee. Is the tee to be counted and the sizing  
> be
> increased as per 5.18.6.2 ?
>
> Any pump experts?
>
> Tony
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to