Other than the turbulence, which was deemed acceptable for the condition
where the relief is piped back to suction under #20, the pipe running from
the tank to the suction side of the pump is the same "chamber" as the tank-
unless there's a OS&Y right on the suction nozzle of the tank- and if you're
running the pump, one would expect that to be open unless you're attempting
high temperature test for air bubble growth- and you'd be better off piping
relief to suction, since if the tank valve was closed, the relief to suction
would be all you've got going into the pump! the relief valve would, of
course, be open sincethe temp elevating would increase pressure on the air
caused by turbulence, assuring a reliable supply of air and water to the
suction side.....

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Friday, March 20, 2009 9:16 AM
To: [email protected]
Subject: RE: Fire Pump relief valve discharge

Any problem dumping the relief discharge back into the tank?

Thank You

Rahe Loftin, P.E.
Region 7 - GSA
Office - 817-978-7299
Fax - 817-978-8644
Cell - 817-371-3102

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to