Now our local AHJ is requiring emergency vents on UL 142 diesel fuel
tanks be vented to outside. And because we will be adding pipe and
fittings between the tank and the vent they want calculations to prove
that the pipe size is adequate and the vent will operate as advertised.
(It seems like only yesterday that we went through the tank overfill
protection with float valves and remote level indicators, now this.)

Their argument is that the tank is "storage" and must comply with IFC
3404 and NFPA #30 even though the tank is connected through a closed
fuel piping system to an oil fired piece of equipment.

My read is that IFC 3401.2(3) references Section 603, 603.1 references
Section 603 and the Int'l Mechanical Code. The Int'l Mechanical code
references NFPA #37. NFPA #37 requires the normal vent to be piped out
side but does not address emergency vents.  

Has anyone out there run into this before and do you or have you piped
emergency vents to outside?

I don't believe this jurisdiction has ever had a fuel tank for a diesel
fire pump involved in a fire so the only history we have is no history.

Thanks in advance for your thoughts.

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ 85024