Working plans are for the installation phase, while the "as-built" set is
intended for use following the installation.  That's why NFPA 13 is silent
on the as-built requirement but it appears in NFPA 25.

I agree this appears somewhat awkward, but I suppose there's logic in there
somewhere.  When you find it, so advise:)

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, March 25, 2009 2:45 PM
To: [email protected]
Subject: Re: Does NFPA 13 require as-built drawings

Okay, but NFPA 25 pertains to maintenance of systems, not  installation.
I understand NFPA is saying: IF there are as-builts, they will be stored,  
etc.
 
Forest  Wilson

Project Manager
Cherokee Fire Protection Co.
3195  Dayton Xenia Rd Ste 900
Dayton OH 45434

ph: 937-376-2333
fx:  614-455-4324
cell: 937-307-5647

Visit our blog: _www.cherokee-fire.blogspot.com_ 
(http://www.cherokee-fire.blogspot.com/)  


FIRE SPRINKLERS SAVE LIVES!!



NOTICE: The information contained in this  email is intended to be solely
for 
the use of the named individual or entity to  which it is directed and may 
contain information that is privileged or otherwise  confidential. It is not

intended for transmission to, or receipt by, anyone  other than the named 
addressee (or a person authorized to deliver it to the  named addressee). It
should 
not be copied or forwarded to any unauthorized  persons. If you have
received 
this electronic mail transmission in error, please  delete it from your
system 
without copying or forwarding it, and notify the  sender of the error by
reply 
email or by calling Cherokee Fire Protection Co. at  888-347-3079 toll free.


 
In a message dated 3/25/2009 5:44:36 P.M. Eastern Daylight Time,  
[email protected] writes:

Actually  you'll find it in NFPA 25 as follows:

" 12.3.2 As-built system  installation drawings, original acceptance test
records, and device  manufacturer's maintenance bulletins shall be retained
to assist in the  proper care of the system and its  components."

_______________________________________________
Sprinklerforum  mailing  list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For  Technical Assistance, send an email to:  [email protected]

To Unsubscribe, send an email  to:[email protected]
(Put the word unsubscribe in  the subject field)


**************Great Deals on Dell 15" Laptops - Starting at $479 
(http://pr.atwola.com/promoclk/100126575x1220635228x1201407499/aol?redir=htt
p:%2F%2Fad.doub
leclick.net%2Fclk%3B213153654%3B34689672%3Bo)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to