Reality check. "As-builts" are a separate document. They are usually 
generated from the original design drawing and the fitter's field 
notes (if he kept them). As to an as-built being exact - good luck. 
Contractors may keep some notes on what they change, but they are 
hardly an EXACT duplicate of what is installed (and the assumption is 
that the designer has access to them). Consequently, as-built 
drawings at best give you an idea of major changes (main and 
sprinkler locations) but are far from perfect. There is not enough 
money or time in any design job for the designer to go out and map 
out every piece of pipe installed. "If pipe lengths and fittings have 
changed..."? Outside of number of heads, what else would change? So 
every job would have to be re-calced. Also, if we have to wait for 
AHJ approval before any changes are made (22.1.2), nothing will ever 
get finished. In a perfect world, you are right, but this ain't a 
perfect world.


At 07:34 PM 3/25/2009, you wrote:
>I think the "as-built" term is a commonly used misnomer, somehow
>distinguishing the document used to install a system from some "extra"
>document you leave behind for the owner to use later.  The proper term
>for "as-built" should be "corrected working plan" representing the
>completion of something that's required from the beginning.  I'm not
>saying the as-built has to be cadded up like the original.  NFPA 13 is
>silent on this.  However, the drawing left behind has to be EXACTLY what
>is installed, and that redlined drawing has to have the AHJ approval in
>some manner (22.1.2).  If pipe lengths or fittings have changed, then
>"corrected hydraulic calculations" are also required.  Otherwise the
>installer has been paid but hasn't completed the job.
>
>Perhaps our frequent AHJ contributors could weigh in on this one as
>well.
>
>Bill Brooks
>
>William N. Brooks, P.E.
>Brooks Fire Protection Engineering Inc.
>372 Wilett Drive
>Severna Park, MD 21146
>410-544-3620 Phone
>410-544-3032 FAX
>412-400-6528 Cell
>
>-------- Original Message --------
>Subject: RE: Does NFPA 13 require as-built drawings
>From: "larryshulman" <[email protected]>
>Date: Wed, March 25, 2009 6:11 pm
>To: <[email protected]>
>
>Working plans are for the installation phase, while the "as-built" set
>is
>intended for use following the installation. That's why NFPA 13 is
>silent
>on the as-built requirement but it appears in NFPA 25.
>
>I agree this appears somewhat awkward, but I suppose there's logic in
>there
>somewhere. When you find it, so advise:)
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of
>[email protected]
>Sent: Wednesday, March 25, 2009 2:45 PM
>To: [email protected]
>Subject: Re: Does NFPA 13 require as-built drawings
>
>Okay, but NFPA 25 pertains to maintenance of systems, not installation.
>I understand NFPA is saying: IF there are as-builts, they will be
>stored,
>etc.
>
>Forest Wilson
>
>Project Manager
>Cherokee Fire Protection Co.
>3195 Dayton Xenia Rd Ste 900
>Dayton OH 45434
>
>ph: 937-376-2333
>fx: 614-455-4324
>cell: 937-307-5647
>
>Visit our blog: _www.cherokee-fire.blogspot.com_
>(http://www.cherokee-fire.blogspot.com/)
>
>
>FIRE SPRINKLERS SAVE LIVES!!
>
>
>
>NOTICE: The information contained in this email is intended to be solely
>for
>the use of the named individual or entity to which it is directed and
>may
>contain information that is privileged or otherwise confidential. It is
>not
>
>intended for transmission to, or receipt by, anyone other than the named
>addressee (or a person authorized to deliver it to the named addressee).
>It
>should
>not be copied or forwarded to any unauthorized persons. If you have
>received
>this electronic mail transmission in error, please delete it from your
>system
>without copying or forwarding it, and notify the sender of the error by
>reply
>email or by calling Cherokee Fire Protection Co. at 888-347-3079 toll
>free.
>
>
>
>In a message dated 3/25/2009 5:44:36 P.M. Eastern Daylight Time,
>[email protected] writes:
>
>Actually you'll find it in NFPA 25 as follows:
>
>" 12.3.2 As-built system installation drawings, original acceptance test
>records, and device manufacturer's maintenance bulletins shall be
>retained
>to assist in the proper care of the system and its components."
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to:
>[email protected]
>
>To Unsubscribe, send an email
>to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>
>**************Great Deals on Dell 15" Laptops - Starting at $479
>(http://pr.atwola.com/promoclk/100126575x1220635228x1201407499/aol?redir=htt
>p:%2F%2Fad.doub
>leclick.net%2Fclk%3B213153654%3B34689672%3Bo)
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to:
>[email protected]
>
>To Unsubscribe, send an email
>to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to:
>[email protected]
>
>To Unsubscribe, send an email
>to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to