Im not sure but are we saying that the dry system also supplies the heads IN 
the top floor dwelling / client rooms ???

There is currently no listed residential sprinkler for dry systems nor the DPV 
.... the use of dry systems in 13 for residential occupancies requires water 
delivery time of 15 seconds ..... The NFPA 13 committee put in the permission 
to do dry residential systems but with the 15 seconds ahead of any such 
equipment being made just in case it came out before the next cycle.  During a 
test burn we intentionally left water off for one minute past the head fusing 
just to see .... it didnt go well and the room was beyond the permissible 
tenability standards of UL1626 prior to suppression.  In other words ..... you 
can do it currently - maybe someday in the future.

The attic alone could be a dry system under the rules but if they also drop 
into the living space we have a problem.  

Dave P.
An AHJ in NJ