Art,

Where does the 15 seconds come from? I can't find anything in 13. Is
it 101? is it a local requirement?

On Mon, Mar 30, 2009 at 2:24 PM, Arthur Tiroly <[email protected]> wrote:
> I may be over thinking this problem. But I see an elderly person in a wheel
> chair that can care fore himself but may not move very fast in an emergency.
> Dry system activation will delay water application resulting in a longer
> pre-burn and a more likely poor outcome to the survivor. That's why we have
> wet residential QR systems. Also why we have a 15 sec. water deliver
> requirement.
>
> Arthur Tiroly
> ATCO Fire Protection Design
> Tiroly and Associates
> 3300 King Ave
> Cleveland, OH 44114
> 216-621-8899
> 216-570-7030 cell
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Todd Williams
> Sent: Monday, March 30, 2009 4:50 PM
> To: [email protected]
> Subject: RE: RESIDENTIAL OCCOPANCY DRY SYSTEM
>
> Maybe I'm missing something here. This is a full NFPA 13 and it would
> be considered a Light Hazard occupancy. It is fed from a dry system
> so you would design the system based on a 1950 sqft area. QR
> sprinklers are also required in all Light Hazard occupancies. What is
> the issue?
>
> You said "It is my understanding that sprinklers in an elderly
> housing assisted living apartment facility is primarily life safety."
> Why? Is there some Code issue that is driving this? Life safety is an
> obvious part of what we do, but in a full NFPA 13 system, property
> protection is added in as well. NFPA 13R  (and 13D) are primarily
> life safety standards, but 13 is the full monty. Is there some
> evidence out there that the delay caused by dry systems is having
> impact on life safety?
>
> Remember life safety systems typically discharge at 0.05 gpm/sqft and
> LH systems at 0.10 gpm/sqft. That is a lot more water out of an LH
> system. Could not the additional water make up for the delay due to
> evacuating the air?
>
> Of course the question I've had is if a sprinkler on a dry system
> activates relatively close to the fire, does the rush of air from the
> sprinkler actually make the fire more intense?
>
>
>
>
> At 04:13 PM 3/30/2009, you wrote:
>>The residential units are supplied from a dry system located in the attic.
>>That was the whole basis for my question. I felt the dry system would take
>>too long to get water to the sprinklers in the residential units. Thanks
> for
>>your input.
>>
>>Arthur Tiroly
>>ATCO Fire Protection Design
>>Tiroly and Associates
>>3300 King Ave
>>Cleveland, OH 44114
>>216-621-8899
>>216-570-7030 cell
>>
>>-----Original Message-----
>>From: [email protected]
>>[mailto:[email protected]] On Behalf Of Dave
>>Sent: Monday, March 30, 2009 1:29 PM
>>To: Sprinkler Forum
>>Subject: RE: RESIDENTIAL OCCOPANCY DRY SYSTEM
>>
>>Im not sure but are we saying that the dry system also supplies the heads
> IN
>>the top floor dwelling / client rooms ???
>>
>>There is currently no listed residential sprinkler for dry systems nor the
>>DPV .... the use of dry systems in 13 for residential occupancies requires
>>water delivery time of 15 seconds ..... The NFPA 13 committee put in the
>>permission to do dry residential systems but with the 15 seconds ahead of
>>any such equipment being made just in case it came out before the next
>>cycle.  During a test burn we intentionally left water off for one minute
>>past the head fusing just to see .... it didnt go well and the room was
>>beyond the permissible tenability standards of UL1626 prior to suppression.
>>In other words ..... you can do it currently - maybe someday in the future.
>>
>>The attic alone could be a dry system under the rules but if they also drop
>>into the living space we have a problem.
>>
>>Dave P.
>>An AHJ in NJ
>>_______________________________________________
>>Sprinklerforum mailing list
>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>For Technical Assistance, send an email to: [email protected]
>>
>>To Unsubscribe, send an email to:[email protected]
>>(Put the word unsubscribe in the subject field)
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>For Technical Assistance, send an email to: [email protected]
>>
>>To Unsubscribe, send an email to:[email protected]
>>(Put the word unsubscribe in the subject field)
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> www.fpdc.com
> 860.535.2080
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....