true but the text is weakly worded. The section that references the Table says "based on the hazard" not the type of sprinkler (as does the Table). I believe the intent was for residential sprinklers (for which a 15 sec requirement exists as part of the listing test standard) but writing what you mean can be a challenge. As pointed out by Ed, the 2010 clarifies it nicely. It was an interesting evolution. It started with the standard dry pipe rule: 60 sec for systems greater than 500 gal and said any size system protecting residential dwellings shall not exceed 60 sec. Then it was pushed down to 15 sec.
Roland On Mar 31, 2009, at 9:29 AM, Thom McMahon wrote: > This requirement for 15 Sec. delivery in residential dry systems > already > exists in NFPA 13 2007, Table 7.2.3.6.1 > > Thom McMahon, SET _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)