true but the text is weakly worded.  The section that references the  
Table says "based on the hazard" not the type of sprinkler (as does  
the Table).  I believe the intent was for residential sprinklers (for  
which a 15 sec requirement exists as part of the listing test  
standard) but writing what you mean can be a challenge.  As pointed  
out by Ed, the 2010 clarifies it nicely.  It was an interesting  
evolution.  It started with the standard dry pipe rule: 60 sec for  
systems greater than 500 gal and said any size system protecting  
residential dwellings shall not exceed 60 sec.  Then it was pushed  
down to 15 sec.

Roland

On Mar 31, 2009, at 9:29 AM, Thom McMahon wrote:

> This requirement for 15 Sec. delivery in residential dry systems  
> already
> exists in NFPA 13 2007, Table 7.2.3.6.1
>
> Thom McMahon, SET