Forgot, there are two other standipipes (size unknown) 3 stories with 
2-1/2" hose valves.



At 08:00 AM 4/6/2009, you wrote:
>Determining age is a difficult task. There have been several
>additions and modifications to the system with very little record
>keeping. From an FIA plan, the oldest building is 1932. There are
>additions dated 1955, 1967, 1973 and one that was erected after the
>date of the plan, which is 1975. Even the plan isn't clear on where
>one stops and the other begins. Most of the appendages are labeled
>"addition" or "wing", so as to what constitutes a different building
>is probably a good question.
>
>There is one 2-1/2", 5-story standpipe with 1-1/2" FHV and one
>2-1/2", 4 story standpipe with 1-1/2" FHV. I believe that these are
>both part of the 1932 building. There is one 2-1/2", 5-story
>standpipe with 2-1/2" FHV. I'm not sure the age of that building. One
>3-story building with 2-1/2" FHV fed from a 4" combination riser
>(buried in wall. I believe that is 4". The rest are fed from
>'horizontal standpipes' on the level where the service enters or a
>fed from sprinkler mains. Three of the standpipes are interconnected,
>but there are also sprinkler risers that are interconnected, so I'm
>not sure (at this point) what is connected to what. I'm getting close, though.
>
>
>
>
>
>At 04:57 PM 4/5/2009, you wrote:
> >Sounds like your first task is to map the standpipes, since they are buried
> >in walls. (Unless accurate as-built drawings exist.) The easiest way we've
> >found to do this is with an underground locator, with an induction signal.
> >(Similar to a line locator the utilities use.) You can rent these at some
> >rental supply places.) Once you confirm what connects to what, some
> >exploratory holes will have to be made to verify pipe size. See Snake tech.
> >by Ridgid tool co makes this a easier task, with less cleanup or repair to
> >rated wall assemblies. Even so you're not going to know where every fitting
> >is, so be generous in your calc's for Phantom fitting loss. Calc's are
> >required because even the old requirement was 65Psi at the top, and current
> >requirements are for 100Psi. If you static on the supply is only 60, it
> >didn't meet code when it was installed if the building is newer than 1963.
> >(I believe that was when the 65Psi was required in 14.)
> >Sounds like calc's for Manual wet standpipe or fire pump for automatic.
> >
> >Thom McMahon, SET
> >Firetech, Inc.
> >2560 Copper Ridge Dr
> >P.O. Box 882136
> >Steamboat Springs, CO 80488
> >Tel:  970-879-7952
> >Fax: 970-879-7926
> >
> >
> >-----Original Message-----
> >From: [email protected]
> >[mailto:[email protected]] On Behalf Of Todd Williams
> >Sent: Friday, April 03, 2009 4:40 PM
> >To: [email protected]
> >Subject: Standpipe dilemma
> >
> >I think I referenced this project in a previous post, but I have now got the
> >whole place mapped out (I think) and need some input on solutions.
> >
> >The facility is a hospital. The interconnected buildings range from 1 to 6
> >stories on a side hill. On the south side, you enter at floor 1; the north
> >side floor 3. Three separate lead-ins, two non-interconnected connections to
> >the public supply. The building is only partially sprinklered. Static
> >pressure is approximately 60 psi
> >
> >There are multiple standpipe/hose valve connections. Some, but not all, are
> >fed from dedicated standpipe lines. Hose valves in cabinets in hallways.
> >
> >6th Floor - no hose connections (mechanical and support areas only) 5th
> >Floor - one 2-1/2" valve, one 1-1/2" valve 4th floor - three 2-1/2" valves,
> >one 1-1/2" valve 3rd Floor - four 2-1/2" valves, one 1-1/2" valve 2nd Floor
> >- four 2-1/2" valves, three 1-1/2" valves 1st Floor - five 2-1/2" valves,
> >two 1-1/2" valves.
> >
> >Some 2-1/2" valves have 1-1/2" reducers, some do not. Most all riser piping
> >is buried behind the walls and not in stairways. Not easily accessible for
> >replacement
> >
> >One riser goes 5 floors, some go three, some valves a fed from horizontal
> >mains on floors where the service enters.
> >
> >They are being required by the State to test the standpipes. My task is to
> >figure out the standpipe criteria and design a system so that the criteria
> >can be met.
> >
> >Any thoughts on what the design criteria would be for this system?
> >
> >Todd G. Williams, PE
> >Fire Protection Design/Consulting
> >Stonington, Connecticut
> >www.fpdc.com
> >860.535.2080
> >_______________________________________________
> >Sprinklerforum mailing list
> >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, Connecticut
>www.fpdc.com
>860.535.2080
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to