Members, Perhaps this will help;

2006 IFC Section 508 Fire Protection Water Supplies

508.5.1 Where required.

Where a portion of the facility or building hereafter constructed or moved
into or within the jurisdiction is more than 400 feet (122 m) from a hydrant
on a fire apparatus access road, as measured by an approved route around the
exterior of the facility or building, on-site fire hydrants and mains shall
be provided where required by the fire code official.

Exceptions:
1.      For Group R-3 and Group U occupancies, the distance requirement
shall be 600 feet (183 m).
2.      For buildings equipped throughout with an approved automatic
sprinkler system installed in accordance with Section   903.3.1.1 (NFPA-13)
or 903.3.1.2, (NFPA-13R) the distance requirement shall be 600 feet (183 m).

Don't forget about 2006 IFC Appendix B and C if adopted in your
jurisdiction.

Sincerely

John Drucker
Fire Protection Subcode Official