Agreed. However, this jurisdiction applies this to sprinkler systems as
well. 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Forest
Wilson
Sent: Wednesday, April 08, 2009 1:34 PM
To: [email protected]
Subject: Re: 100ft from FDC to hydrant?

For standpipe systems only.    No requirement for sprinkler it is local
ahj decision. 
Forest Wilson 

-----Original Message-----
From: "Smith, Steven D. (CSFD)" <[email protected]>

Date: Wed, 8 Apr 2009 13:31:04
To: <[email protected]>
Subject: RE: 100ft from FDC to hydrant?


There shall be a fire hydrant capable of supplying the fire flow
requirements for the system within 100 feet of the FDC.  (NFPA
14:6.4.5.4) 