There shall be a fire hydrant capable of supplying the fire flow
requirements for the system within 100 feet of the FDC.  (NFPA
14:6.4.5.4) 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, April 08, 2009 1:19 PM
To: [email protected]
Subject: 100ft from FDC to hydrant?

Got a comment about locating a fire hydrant no more than 75-100 ft from
the riser FDC.

I know I've seen this requirement somewhere but for some reason I can
not locate it in NFPA or the IBC or IFC.  Does anyone know where this is
right off the top of their head?

All my search engines have failed me.  

Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 