Chris, In jails I've seen electrically operated zone valves with a 90 second time delay before the valves were opened, an "open now" override, and an abort to each valve but that required CCTV and a constantly manned station wherein the operator had complete control over the cameras and operation of the valves. These are always on wet systems and I'd suspect that they required a PE to bless them.
On Mon, Apr 6, 2009 at 2:15 PM, Chris Cahill <[email protected]> wrote: > Can one have an abort button on a double interlock pre-action > (electric/pneumatic)? I'm assuming it would be like on a clean agent > system. PE hasn't got back to us (don't really expect him to, not a > surprise). > > > > Chris Cahill, P.E. > > Fire Protection Engineer > > Sentry Fire Protection, Inc. > > > > 763-658-4483 > > 763-658-4921 fax > > > > Email: [email protected] > > > > Mail: P.O. Box 69 > > Waverly, MN 55390 > > > > Location: 4439 Hwy 12 SW > > Waverly, MN 55390 > > > > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman at home.... _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)