But where does the UL rank in order?  By this I mean if the local area has 
adopted 13 and 25 do they also have to take into account ULs rules or just say 
as long as the device is listed it is good?




________________________________
From: Mike Henke <[email protected]>
To: [email protected]
Sent: Monday, April 6, 2009 4:45:14 PM
Subject: RE: Pre-action abort

It is prohibited by UL.
UL 864 states: Abort switches shall not be used on systems intended to
perform pre-action or deluge functions.

Regards,

mike

Mike Henke CET
Sprinkler Product Manager
Potter Electric Signal Co. LLC
WWW.POTTERSIGNAL.COM
866-572-3005

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Monday, April 06, 2009 4:29 PM
To: [email protected]
Subject: RE: Pre-action abort

Question one: Why? 
Question two: At what stage of system response do you want to abort?

There is no mention anywhere in NFPA 13 about the allowance or
disallowance of an abort switch.  I just can't see where anyone would be
quick enough to get to it if something in the system started an
operation anyway.  

With all the delays already built in to a double interlock system what
in the world could another interruption accomplish?

I would not be in favor of it.  But for the sake of curiosity, what's
the application and reasoning behind the question?

Craig L. Prahl, CET  
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris
Cahill
Sent: Monday, April 06, 2009 5:15 PM
To: [email protected]
Subject: Pre-action abort

Can one have an abort button on a double interlock pre-action
(electric/pneumatic)?  I'm assuming it would be like on a clean agent
system.  PE hasn't got back to us (don't really expect him to, not a
surprise).  



Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.



763-658-4483

763-658-4921 fax



Email: [email protected]



Mail: P.O. Box 69

        Waverly, MN 55390



Location: 4439 Hwy 12 SW

              Waverly, MN 55390



_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)



      
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to