John,

Potter manufactures a release panel that has a zone that can be
programmed as an abort circuit or a supervisory zone. As part of our
listing we were required by UL to state that the abort circuit on
pre-action and deluge systems is not permitted by UL 864.

In my opinion that means that programming the zone to be an abort
circuit for a pre-action system would mean the panel would not be in
compliance with UL & not be listed for that system.

The statue, regulation or code requiring the abort circuit probably also
requires a listed panel. So the statue, regulation or code would require
something that cannot be accomplished, an abort switch on a listed
pre-action panel.

Regards

mike

Mike Henke CET
Sprinkler Product Manager
Potter Electric Signal Co. LLC
WWW.POTTERSIGNAL.COM
866-572-3005

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John
Drucker
Sent: Tuesday, April 07, 2009 8:20 AM
To: [email protected]
Subject: RE: Pre-action abort

Continuing the discussion, the answer to the question is simple does a
statute, regulation or code prescribe an abort station on a deluge or
preaction system ?

Keep in mind that codes and standards are being written in positive
language, i.e. whats permitted vs negative language, i.e. whats
prohibited. Remember what state I'm from ?, Missouri.

John Drucker 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Sal Izzo
(TECH- 103)
Sent: Tuesday, April 07, 2009 9:04 AM
To: [email protected]
Subject: RE: Pre-action abort

It is true that the laboratory test standards do not fit into the
hierarchy of code enforcement;; however, NFPA 13 requires the products
used in sprinkler systems to be listed.  As Mike stated, UL 864 requires
that  abort switches shall not be used on deluge or preaction systems.
If an abort function is provided and is used on such systems, it would
not meet the functional requirements of the test standard and not be
recognized as listed.  

Salvatore Izzo, P.E.
Manager - Reliable Technical Services


________________________________________
From: [email protected]
[[email protected]] On Behalf Of John Drucker
[[email protected]]
Sent: Tuesday, April 07, 2009 6:29 AM
To: [email protected]
Subject: RE: Pre-action abort

Great question.  Listings don't seem to have the effect one would
assume. We often hear "must be installed in accordance with the
listing", or "product listed for the intended purpose".

Then we see prescriptive code applications such as deck and balcony
sprinklers and smoke alarms used in other then dwelling units. The
government can pretty much do as it pleases in the pursuit of
"safeguarding building occupants and emergency responders"

It's about the hierarchy of code enforcement, it goes something like
this;

1. Statutes = The Legislative action, in NJ the "Uniform Construction
Code Act"
2. Regulations = The Department or Commissioner rule making, in NJ the
"Uniform Construction Code"
3. Codes= The where and when side of the equation, in NJ the 2006 IBC/NJ
Edition, amongst many others.
4. Reference Standards = The how side of the equation, in NJ the 2002
Edition of NFPA-13 for example.
5. Manufacturer's Instructions = The specific how for a specific
product.
6. Listings = The nationally recognized testing lab that evaluated the
product for fitness.

I'm sure there are variants at municipal, county and even federal
levels.

Bottom line if a statute, regulation or code prescribes it then so it
shall be.

Hope that helps,

John Drucker


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jay Jay
Blocker
Sent: Monday, April 06, 2009 11:37 PM
To: [email protected]
Subject: Re: Pre-action abort

But where does the UL rank in order?  By this I mean if the local area
has adopted 13 and 25 do they also have to take into account ULs rules
or just say as long as the device is listed it is good?




________________________________
From: Mike Henke <[email protected]>
To: [email protected]
Sent: Monday, April 6, 2009 4:45:14 PM
Subject: RE: Pre-action abort

It is prohibited by UL.
UL 864 states: Abort switches shall not be used on systems intended to
perform pre-action or deluge functions.

Regards,

mike

Mike Henke CET
Sprinkler Product Manager
Potter Electric Signal Co. LLC
WWW.POTTERSIGNAL.COM
866-572-3005

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Monday, April 06, 2009 4:29 PM
To: [email protected]
Subject: RE: Pre-action abort

Question one: Why?
Question two: At what stage of system response do you want to abort?

There is no mention anywhere in NFPA 13 about the allowance or
disallowance of an abort switch.  I just can't see where anyone would be
quick enough to get to it if something in the system started an
operation anyway.

With all the delays already built in to a double interlock system what
in the world could another interruption accomplish?

I would not be in favor of it.  But for the sake of curiosity, what's
the application and reasoning behind the question?

Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris
Cahill
Sent: Monday, April 06, 2009 5:15 PM
To: [email protected]
Subject: Pre-action abort

Can one have an abort button on a double interlock pre-action
(electric/pneumatic)?  I'm assuming it would be like on a clean agent
system.  PE hasn't got back to us (don't really expect him to, not a
surprise).



Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.



763-658-4483

763-658-4921 fax



Email: [email protected]



Mail: P.O. Box 69

        Waverly, MN 55390



Location: 4439 Hwy 12 SW

              Waverly, MN 55390



_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)




_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or
entity to which it is addressed and may contain information that is
privileged and confidential, nor is it, unless specifically stated,
intended to be relied upon by any person or persons other than the
individual or entity named above and no warranties or representations
are made or intended to persons or entities not named above.  If the
reader is not the intended recipient, you are hereby notified that any
dissemination, distribution or copying of this communication is strictly
prohibited.  If you have received this communication in error, please
notify us immediately by telephone, return this message to the address
above and delete all copies.  Thank you.

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to