Subject: Re: Pre-action abort


But UL is the entity doing the listing.
 Forest Wilson
 
 -----Original Message-----
 From: Jay Jay Blocker <[email protected]>
 
 Date: Mon, 6 Apr 2009 20:36:49
 To: <[email protected]>
 Subject: Re: Pre-action abort
 
 
 But where does the UL rank in order?  By this I mean if the local area has 
adopted 13 and 25 do they also have to take into account ULs rules or just say 
as long as the device is listed it is good?
 
 
 
 
 ________________________________
 From: Mike Henke <[email protected]>
 To: [email protected]
 Sent: Monday, April 6, 2009 4:45:14 PM
 Subject: RE: Pre-action abort
 
 It is prohibited by UL.
 UL 864 states: Abort switches shall not be used on systems intended to
 perform pre-action or deluge functions.
 
 Regards,
 
 mike
 
 Mike Henke CET
 Sprinkler Product Manager
 Potter Electric Signal Co. LLC
 WWW.POTTERSIGNAL.COM
 866-572-3005
 
 -----Original Message-----
 From: [email protected]
 [mailto:[email protected] 
<mailto:[email protected]> ] On Behalf Of
 [email protected]
 Sent: Monday, April 06, 2009 4:29 PM
 To: [email protected]
 Subject: RE: Pre-action abort
 
 Question one: Why?
 Question two: At what stage of system response do you want to abort?
 
 There is no mention anywhere in NFPA 13 about the allowance or
 disallowance of an abort switch.  I just can't see where anyone would be
 quick enough to get to it if something in the system started an
 operation anyway. 
 
 With all the delays already built in to a double interlock system what
 in the world could another interruption accomplish?
 
 I would not be in favor of it.  But for the sake of curiosity, what's
 the application and reasoning behind the question?
 
 Craig L. Prahl, CET 
 Fire Protection Specialist
 Mechanical Department
 CH2MHILL
 Lockwood Greene
 1500 International Drive
 PO Box 491, Spartanburg, SC  29304-0491
 Direct - 864.599.4102
 Fax - 864.599.8439
 [email protected]
 http://www.ch2m.com <http://www.ch2m.com> 
 
 
 -----Original Message-----
 From: [email protected]
 [mailto:[email protected] 
<mailto:[email protected]> ] On Behalf Of Chris
 Cahill
 Sent: Monday, April 06, 2009 5:15 PM
 To: [email protected]
 Subject: Pre-action abort
 
 Can one have an abort button on a double interlock pre-action
 (electric/pneumatic)?  I'm assuming it would be like on a clean agent
 system.  PE hasn't got back to us (don't really expect him to, not a
 surprise). 
 
 
 
 Chris Cahill, P.E.
 
 Fire Protection Engineer
 
 Sentry Fire Protection, Inc.
 
 
 
 763-658-4483
 
 763-658-4921 fax
 
 
 
 Email: [email protected]
 
 
 
 Mail: P.O. Box 69
 
         Waverly, MN 55390
 
 
 
 Location: 4439 Hwy 12 SW
 
               Waverly, MN 55390
 
 
 
 _______________________________________________
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
<http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> 
 For Technical Assistance, send an email to:
 [email protected]
 
 To Unsubscribe, send an email
 to:[email protected]
 (Put the word unsubscribe in the subject field)
 _______________________________________________
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
<http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> 
 For Technical Assistance, send an email to:
 [email protected]
 
 To Unsubscribe, send an email
 to:[email protected]
 (Put the word unsubscribe in the subject field)
 _______________________________________________
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
<http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> 
 For Technical Assistance, send an email to: [email protected]
 
 To Unsubscribe, send an email to:[email protected]
 (Put the word unsubscribe in the subject field)
 
 
 
      
 _______________________________________________
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
<http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> 
 For Technical Assistance, send an email to: [email protected]
 
 To Unsubscribe, send an email to:[email protected]
 (Put the word unsubscribe in the subject field)
 _______________________________________________
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
<http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> 
 For Technical Assistance, send an email to: [email protected]
 
 To Unsubscribe, send an email to:[email protected]
 (Put the word unsubscribe in the subject field)
 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to