This is another "Outside the scope of NFPA 13" Situations. Obviously input
from the sprinkler MFG.'s is good but they will be reluctant to take any
design responsibility for conditions not defined by NFPA 13, or confirmed by
testing. Time to hire a "Good" FPE.

Even if you just look at Fig. 14.2.4.3, you'll see for 35 foot height you'd
need over 200% design density if the graph even went that high. Then you
have the additional problem of delayed response for the ceiling height
outside of the scope. How do you allow for that? 2x or 3x the design area?
You may even be looking at something other than "Control Mode" protection.
Deluge? HE Foam? IR detection?

Time for professional help outside of the "proscriptive Standard".

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Daniel Merkle
Sent: Friday, April 10, 2009 9:06 AM
To: [email protected]
Subject: Storage Sprinkler

Anyone know of a storage sprinkler to protect a 62'-0" high building with
solid pile Class 1 storage, stored to 36'-0"? 

 Daniel L. Merkle, CET 


      
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to