Just out of curiosity, what is the Class I product they are storing 
solid piled to 24'?



At 12:17 PM 4/10/2009, you wrote:
>Sorry, storage hight is 24'-0 which would give me 130% per 
>14.2.4.3.  My concern is the 38'-0" of open space to the roof.  What 
>if the roof was 100ft. high?
>
>  Daniel L. Merkle, CET
>
>
>
>
>
>
>________________________________
>From: Thom McMahon <[email protected]>
>To: [email protected]
>Sent: Friday, April 10, 2009 11:46:19 AM
>Subject: RE: Storage Sprinkler
>
>This is another "Outside the scope of NFPA 13" Situations. Obviously input
>from the sprinkler MFG.'s is good but they will be reluctant to take any
>design responsibility for conditions not defined by NFPA 13, or confirmed by
>testing. Time to hire a "Good" FPE.
>
>Even if you just look at Fig. 14.2.4.3, you'll see for 35 foot height you'd
>need over 200% design density if the graph even went that high. Then you
>have the additional problem of delayed response for the ceiling height
>outside of the scope. How do you allow for that? 2x or 3x the design area?
>You may even be looking at something other than "Control Mode" protection.
>Deluge? HE Foam? IR detection?
>
>Time for professional help outside of the "proscriptive Standard".
>
>Thom McMahon, SET
>Firetech, Inc.
>2560 Copper Ridge Dr
>P.O. Box 882136
>Steamboat Springs, CO 80488
>Tel:  970-879-7952
>Fax: 970-879-7926
>
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Daniel Merkle
>Sent: Friday, April 10, 2009 9:06 AM
>To: [email protected]
>Subject: Storage Sprinkler
>
>Anyone know of a storage sprinkler to protect a 62'-0" high building with
>solid pile Class 1 storage, stored to 36'-0"?
>
>Daniel L. Merkle, CET
>
>
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>
>
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to