Listen to Steve but support it with the 2010 ROC. We did a lot of work to explicitly address excessive clearance for spray sprinklers in storage under section 12.1.3.4 currently titled Ceiling Heights (changed that too). The current criteria won't fly because it is limited to solid pile (as shown by the approach coming from the old NFPA 231) and Class I-IV in racks less than 25 ft (though that became clear only at the ROC). Section 12.1 kills using it for all storage. The option to put a barrier over the rack with sprinkler beneath them (tough option) was deleted.
Roland On Apr 10, 2009, at 9:21 AM, Steve Leyton wrote: > In-racks baby! Sell sprinkers! > > Steve Leyton > Protection Design & Consulting > San Diego, CA _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)