I don't think there is a limit for area density designs so it is within
the scope of #13. Your concern is well placed but the alternative is a
performance based design. It's only a Class I so I would just go with
the prescriptive area density for the commodity and height. 

Ron Fletcher
Aero Automatic Sprinkler
21605 N. Central Ave
Phoenix, AZ 85024
P: 623.580.7836
F: 623.434.3420
C: 602.763.4160

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Daniel
Merkle
Sent: Friday, April 10, 2009 10:01 AM
To: [email protected]
Subject: Re: Storage Sprinkler

Ron, 
 You are correct. It is solid pile and what concerns me is I could not
find any limit on clearance from top of storage.





________________________________
From: "Fletcher, Ron" <[email protected]>
To: [email protected]
Sent: Friday, April 10, 2009 12:57:20 PM
Subject: RE: Storage Sprinkler

He said it was solid pile. Is there a limit on clearance from top of
storage for area density in 07?

Ron Fletcher
Aero Automatic Sprinkler
21605 N. Central Ave
Phoenix, AZ 85024
P: 623.580.7836
F: 623.434.3420
C: 602.763.4160

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Friday, April 10, 2009 9:49 AM
To: [email protected]
Subject: Re: Storage Sprinkler

Listen to Steve but support it with the 2010 ROC.  We did a lot of  
work to explicitly address excessive clearance for spray sprinklers in  
storage under section 12.1.3.4 currently titled Ceiling Heights  
(changed that too).  The current criteria won't fly because it is  
limited to solid pile (as shown by the approach coming from the old  
NFPA 231) and Class I-IV in racks less than 25 ft (though that became  
clear only at the ROC).  Section 12.1 kills using it for all  
storage.   The option to put a barrier over the rack with sprinkler  
beneath them (tough option) was deleted.

Roland

On Apr 10, 2009, at 9:21 AM, Steve Leyton wrote:

> In-racks baby!   Sell sprinkers!
>
> Steve Leyton
> Protection Design & Consulting
> San Diego, CA

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)



      
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to