Roland,
I see what you are talking about in 12.1.3.4.1(2007).
What if you are still using 2002?

 Daniel L. Merkle, CET 






________________________________
From: Roland Huggins <[email protected]>
To: [email protected]
Sent: Friday, April 10, 2009 1:14:06 PM
Subject: Re: Storage Sprinkler

As the criteria says, you artificially assign a storage height so that  
you have a 20 ft clearance.  That is inherently limited, though, by  
solid pile having a maximum storage height so a 50 ft ceiling is about  
it.  Beyond that you are then back to the previously mentioned ceiling  
installation business.

Roland

On Apr 10, 2009, at 10:00 AM, Daniel Merkle wrote:

> Ron,
> You are correct. It is solid pile and what concerns me is I could  
> not find any limit on clearance from top of storage.
>
>
>
>
>
> ________________________________
> From: "Fletcher, Ron" <[email protected]>
> To: [email protected]
> Sent: Friday, April 10, 2009 12:57:20 PM
> Subject: RE: Storage Sprinkler
>
> He said it was solid pile. Is there a limit on clearance from top of
> storage for area density in 07?
>
> Ron Fletcher
> Aero Automatic Sprinkler
> 21605 N. Central Ave
> Phoenix, AZ 85024
> P: 623.580.7836
> F: 623.434.3420
> C: 602.763.4160
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Roland
> Huggins
> Sent: Friday, April 10, 2009 9:49 AM
> To: [email protected]
> Subject: Re: Storage Sprinkler
>
> Listen to Steve but support it with the 2010 ROC.  We did a lot of
> work to explicitly address excessive clearance for spray sprinklers in
> storage under section 12.1.3.4 currently titled Ceiling Heights
> (changed that too).  The current criteria won't fly because it is
> limited to solid pile (as shown by the approach coming from the old
> NFPA 231) and Class I-IV in racks less than 25 ft (though that became
> clear only at the ROC).  Section 12.1 kills using it for all
> storage.   The option to put a barrier over the rack with sprinkler
> beneath them (tough option) was deleted.
>
> Roland
>
> On Apr 10, 2009, at 9:21 AM, Steve Leyton wrote:
>
>> In-racks baby!   Sell sprinkers!
>>
>> Steve Leyton
>> Protection Design & Consulting
>> San Diego, CA
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to:
> [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)



      
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to