George,

I don't recall it being described as "big insulated panel box.' In
fact I think Tony said he hadn't seen it. Go back a post or two. My
thought is that if this thing is a factory manufactured device  that
is brought out on a truck, dropped off and plugged-in (even if it
comes in large sub-assemblies that just plug into each other) then
it's a big reefer and not a room or space.

On Fri, Apr 24, 2009 at 8:02 AM, George Church <[email protected]> wrote:
> Sounds like it ought to be treated more like a walkin box to me, despite the
> lack of walk-in. Its still a big insulated panel box full of product.
> Since hte product is pretty non-flam, maybe local AHJ, etc would bless
> omitting
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Ron Greenman
> Sent: Friday, April 24, 2009 10:11 AM
> To: [email protected]
> Subject: Re: Walk-in cooler
>
> George,
>
> This is a dispensing unit and I doubt we'd dispense flammable liquids
> from a similar device. Sprinklers in this case, I believe, would be
> similar to sprinklering the inside of the entertainment center because
> it's big or the dresser because it's a storage facility for textile
> products in transit. That is, of course, if Tony's unit is just a big
> refrigerator.
>
> On Fri, Apr 24, 2009 at 5:02 AM, George Church <[email protected]> wrote:
>> Would we consider different treatment if it were stocked with combustibles
>> or flammable liquids?
>>
>> glc
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Ron
> Greenman
>> Sent: Friday, April 24, 2009 1:40 AM
>> To: [email protected]
>> Subject: Re: Walk-in cooler
>>
>> Tony,
>>
>> I like the idea that it may be a large appliance. We don't sprinkler
>> the Coke machine or the Red Bull machine. Is this thing constructed on
>> site or is it brought in as a unit. If the latter and since you can't
>> walk in I'd call it an appliance and not a room (or space).
>>
>> On Thu, Apr 23, 2009 at 8:15 PM, A.P.Silva <[email protected]> wrote:
>>> Haven't seen the cooler. Someone asked me whether it should be
>> sprinklered.
>>> I will have to find out, but meanwhile I'm guessing it is stocked from
>>> behind, the same as milk coolers in stores. Cooler inside or outside? Not
>>> sure if I understand the question and its significance. Being a beer
>> cooler,
>>> it would be cooler inside than outside.
>>>
>>> Tony
>>>
>>> -----Original Message-----
>>> From: [email protected]
>>> [mailto:[email protected]] On Behalf Of Todd
>> Williams
>>> Sent: April 23, 2009 2:35 PM
>>> To: [email protected]
>>> Subject: RE: Walk-in cooler
>>>
>>> Is it stocked from the front or is there a walkway behind the pickers?
>>> Cooler inside or outside?
>>>
>>>
>>>
>>> At 04:17 PM 4/23/2009, you wrote:
>>>>An update as I've additional information.
>>>>
>>>>The cooler is 30' long 4' wide and 7' high. It has glass doors and open
>>>>metal shelves. So you grab the beer closest to you and the next one
> slides
>>>>forward. When stocked full, there is hardly any empty space inside. You
>>>>might see similar ones in stores that sell liqour. Does it have to be
>>>>sprinklered?
>>>>
>>>>Tony
>>>>
>>>>-----Original Message-----
>>>>From: [email protected]
>>>>[mailto:[email protected]] On Behalf Of Forest
>>> Wilson
>>>>Sent: April 23, 2009 12:48 PM
>>>>To: [email protected]
>>>>Subject: Re: Walk-in cooler
>>>>
>>>>They can also shut down the cooler and use for general storage.
>>>>I saw one after it burned. It was like a crushed can.
>>>>Forest Wilson
>>>>
>>>>-----Original Message-----
>>>>From: "A.P.Silva" <[email protected]>
>>>>
>>>>Date: Thu, 23 Apr 2009 11:16:20
>>>>To: <[email protected]>
>>>>Subject: RE: Walk-in cooler
>>>>
>>>>
>>>>Exactly, though one difference may be in this case, the storage quantity
>>> may
>>>>be more. I think this is a grey area in NFPA. We provide heads in walk-in
>>>>freezers and coolers. But what are the chances for a fire inside these?
>>>>Haven't heard of any, but I suppose there could be an electrical fault
>> that
>>>>could start a fire.
>>>>
>>>>Tony
>>>>
>>>>-----Original Message-----
>>>>From: [email protected]
>>>>[mailto:[email protected]] On Behalf Of Chris
>> Cahill
>>>>Sent: April 23, 2009 11:02 AM
>>>>To: [email protected]
>>>>Subject: RE: Walk-in cooler
>>>>
>>>>Doesn't sound much different than the milk cooler or pop cooler or the
>>>>freezer isle in a grocery or Qwik Mart.  Never saw sprinklers in these.
>>>>Argument is it's large appliance.
>>>>
>>>>Chris Cahill, P.E.
>>>>Fire Protection Engineer
>>>>Sentry Fire Protection, Inc.
>>>>
>>>>763-658-4483
>>>>763-658-4921 fax
>>>>
>>>>Email: [email protected]
>>>>
>>>>Mail: P.O. Box 69
>>>>         Waverly, MN 55390
>>>>
>>>>Location: 4439 Hwy 12 SW
>>>>               Waverly, MN 55390
>>>>-----Original Message-----
>>>>From: [email protected]
>>>>[mailto:[email protected]] On Behalf Of A.P.Silva
>>>>Sent: Thursday, April 23, 2009 11:14 AM
>>>>To: [email protected]
>>>>Subject: Walk-in cooler
>>>>
>>>>Generally the industry practice (from what I know) is to provide
>> sprinklers
>>>>in walk-in coolers and freezers. The cooler I am looking at is a beer
>>> cooler
>>>>approx. 30 feet long, 10 feet deep and 7 feet high. It is full with
>>> shelves,
>>>>and no one could "walk-in". Would it have to be sprinklered? Anyone has
>>> come
>>>>across a similar situation or have any opinions?
>>>>
>>>>Tony
>>>>
>>>>_______________________________________________
>>>>Sprinklerforum mailing list
>>>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>For Technical Assistance, send an email to: [email protected]
>>>>
>>>>To Unsubscribe, send an email to:[email protected]
>>>>(Put the word unsubscribe in the subject field)
>>>>
>>>>_______________________________________________
>>>>Sprinklerforum mailing list
>>>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>For Technical Assistance, send an email to: [email protected]
>>>>
>>>>To Unsubscribe, send an email to:[email protected]
>>>>(Put the word unsubscribe in the subject field)
>>>>
>>>>_______________________________________________
>>>>Sprinklerforum mailing list
>>>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>For Technical Assistance, send an email to: [email protected]
>>>>
>>>>To Unsubscribe, send an email to:[email protected]
>>>>(Put the word unsubscribe in the subject field)
>>>>_______________________________________________
>>>>Sprinklerforum mailing list
>>>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>For Technical Assistance, send an email to: [email protected]
>>>>
>>>>To Unsubscribe, send an email to:[email protected]
>>>>(Put the word unsubscribe in the subject field)
>>>>
>>>>_______________________________________________
>>>>Sprinklerforum mailing list
>>>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>For Technical Assistance, send an email to: [email protected]
>>>>
>>>>To Unsubscribe, send an email to:[email protected]
>>>>(Put the word unsubscribe in the subject field)
>>>
>>> Todd G. Williams, PE
>>> Fire Protection Design/Consulting
>>> Stonington, Connecticut
>>> www.fpdc.com
>>> 860.535.2080
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>>
>>
>>
>>
>> --
>> Ron Greenman
>> at home....
>> _______________________________________________
>> Sprinklerforum mailing list
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
> --
> Ron Greenman
> at home....
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....