Is it stocked from the front or is there a walkway behind the 
pickers? Cooler inside or outside?



At 04:17 PM 4/23/2009, you wrote:
>An update as I've additional information.
>
>The cooler is 30' long 4' wide and 7' high. It has glass doors and open
>metal shelves. So you grab the beer closest to you and the next one slides
>forward. When stocked full, there is hardly any empty space inside. You
>might see similar ones in stores that sell liqour. Does it have to be
>sprinklered?
>
>Tony
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Forest Wilson
>Sent: April 23, 2009 12:48 PM
>To: [email protected]
>Subject: Re: Walk-in cooler
>
>They can also shut down the cooler and use for general storage.
>I saw one after it burned. It was like a crushed can.
>Forest Wilson
>
>-----Original Message-----
>From: "A.P.Silva" <[email protected]>
>
>Date: Thu, 23 Apr 2009 11:16:20
>To: <[email protected]>
>Subject: RE: Walk-in cooler
>
>
>Exactly, though one difference may be in this case, the storage quantity may
>be more. I think this is a grey area in NFPA. We provide heads in walk-in
>freezers and coolers. But what are the chances for a fire inside these?
>Haven't heard of any, but I suppose there could be an electrical fault that
>could start a fire.
>
>Tony
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Chris Cahill
>Sent: April 23, 2009 11:02 AM
>To: [email protected]
>Subject: RE: Walk-in cooler
>
>Doesn't sound much different than the milk cooler or pop cooler or the
>freezer isle in a grocery or Qwik Mart.  Never saw sprinklers in these.
>Argument is it's large appliance.
>
>Chris Cahill, P.E.
>Fire Protection Engineer
>Sentry Fire Protection, Inc.
>
>763-658-4483
>763-658-4921 fax
>
>Email: [email protected]
>
>Mail: P.O. Box 69
>         Waverly, MN 55390
>
>Location: 4439 Hwy 12 SW
>               Waverly, MN 55390
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of A.P.Silva
>Sent: Thursday, April 23, 2009 11:14 AM
>To: [email protected]
>Subject: Walk-in cooler
>
>Generally the industry practice (from what I know) is to provide sprinklers
>in walk-in coolers and freezers. The cooler I am looking at is a beer cooler
>approx. 30 feet long, 10 feet deep and 7 feet high. It is full with shelves,
>and no one could "walk-in". Would it have to be sprinklered? Anyone has come
>across a similar situation or have any opinions?
>
>Tony
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to