I agree with you there is a lot of wood present and a lot of air spaces.
NFPA defines this commodity as a Class II, if we open the box a little and
just say there is a way to secure these barrels to a conventional wood
pallet and floor stack, it still falls under the criteria of a Class II in
accordance with Section 5.6.3.2 (2007) if I'm not missing something.  This
scenario has a whole lot more wood in it than the cradle method.  If this
arrangement were indeed classified as rack it would have to be portable
rack, my problem then becomes the aisle - it is only 3 feet assuming I had 4
feet my density more than doubles to a .32 in accordance with Table
16.2.1.3.2.

The more I look at this I think the best option would be to treat it as
racked storage, that way there shouldn't be any second guessing.  Thanks for
your input.

Jim Johnston


-----Original Message-----
From: Arthur Tiroly [mailto:[email protected]] 
Sent: Tuesday, May 19, 2009 12:08 PM
To: [email protected]
Subject: RE: Wine Barrel Storage

What I envision is a lot of wood and a lot of air spaces surrounding the
wood barrels and cradles. It seems much more than OH2 storage hazard. Not as
bad as pallet storage but plenty of surfaces to burn when 18ft high. Not as
bad as whiskey barrel warehouse. No answers just more to think about.

Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
3300 King Ave
Cleveland, OH 44114
216-621-8899
216-570-7030 cell


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jim Johnston
Sent: Tuesday, May 19, 2009 2:14 PM
To: [email protected]
Subject: Wine Barrel Storage

Greetings All:

 

Has anybody on this forum designed systems for wine barrel storage?  I'm
guessing the Californians have.  Barrels are in horizontal position, stored
on a cradle,  cradle follows curvature of barrel, cradle / barrel is stacked
6 high total height of 18'.  There is a 6" clearance between stacks i.e top
of barrel to bottom of barrel, small transverse and longitudinal space.  My
gut re-action would be considering this palletized storage versus rack.
When the barrel is picked up so is its corresponding cradle - that's where I
come up with palletize.   Alcohol less than 20% in wood barrels is a class
II.

 

Any input? 

 

Jim Johnston, P.E.

Fire Protection Engineer

Inland Fire Protection, Inc

1100 Ahtanum Road

Yakima, WA 98903

Phone 509-248-4471

Fax 509-248-1180

[email protected]

 

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to