I think a low level system employees strategically located oscillating turret 
nozzles that apply low expansion foam to the floor area under the wings.  I 
would go with low level, but if the die is cast (jacta alea est) with high-ex 
-- blow, go, and be happy.

J. Scott Mitchell, P.E.
JSM Fire Protection Engineering

--- On Sat, 5/30/09, DerBlitzkrieger <[email protected]> wrote:

From: DerBlitzkrieger <[email protected]>
Subject: Low level foam systems
To: [email protected]
Date: Saturday, May 30, 2009, 2:10 AM

Hello,

I'm reviewing the design and installation for a Group I aircraft hangar of
Type I construction.  The plane being worked on is a C-130J-30 and its wing
area doesn't excced 3000 ft², so I only need a sprinkler system, and a low
level low- or high-expansion foam system.

My problem is, I cannot find a definition for what a low-level foam system
is.  IE, max foam generator height, etc.  I've checked NFPA 11, 16, 409, and
the glossary of terms.

That's somewhat academic, as the system designer opted instead to go with a
roof level high expansion foam system using blower type generators, and
using the sprinkler system to actuate the system.

This seems like the total flooding roof level system would be a better
protection route than anything a low-level system could provide.  What do
you think?  And what exactly makes a low-level foam system low-level?

I would appreciate any insight into this.

Thanks,

Ben Young, CET
Fire Protection Construction Lead
DynCorp AFCAP
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)



      
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to