Do these same AHJ's make you do a remote area density flow test, live water
on the floor?  It really is the same thing.  

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brown, Mike
Sent: Wednesday, June 17, 2009 2:31 PM
To: [email protected]
Subject: RE: Slow responding dry pipe valves-FDT

I don't doubt what everyone is saying... I understand the code as Chris
stated... I'm thinking about from some of our local AHJ's perspective. I
have a feeling that some of the "old school" AHJ's could care less about
what the software says and are more concerned with real life results. 

Mike Brown
Project Designer
Sunland Fire Protection
1218 Elon Place 
High Point, NC 27263
Ph. 336.886.7027 Ext. 140
Fax: 336.886.7024
WWW.SUNLANDFIRE.COM

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ken
Holsopple (forum)
Sent: Wednesday, June 17, 2009 3:26 PM
To: [email protected]
Subject: RE: Slow responding dry pipe valves-FDT

Mike Brown wrote:

>But what happens when then software shows the system tripping in the
>required amount of time...then when it comes time for final inspection
>with the AHJ and it doesn't work? That could be costly mistake !?

Mike,

Just went through some FDT training (refresher course) and have been
using
the program for about three years. 

Keep in mind that the program carries a UL Listing. It has been tested
in
comparison with "real world" application and as Chris and others stated
it
is pretty close. The 2007 edition expanded and clarified on the testing
procedures with regards to using the software and testing the system.
You
may want to take a look. The new edition of 25 also had some changes
with
regards to freezer facilities and regular testing of dry systems that
were
designed using the water delivery software.

The new acceptance test/inspection procedures provide guidance to what I
like to equate to a main drain test. Comparison to the previous years
results no matter if they are over 60 seconds or not. It also provides
an
alternate method using a "manifold" with several outlets depending on
the
hazard protected.

Like any other program.....garbage in means garbage out. You have to
mind
your p's and q's, but I would not consider it any worse than running
hydraulic calculations. Just a couple of more variables like air
pressure
and trip ratio for the valve, etc.

And yes, I can say for sure that any mistake I make carries a price tag.
I
keep that in mind every time I input data and hit the calculate button.

Ken Holsopple
Designer
Rowe Sprinkler Systems, Inc.




_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to