Chris wrote:

>Let me clarify, I thought it was way too far off in the 1 example I was
>involved with.  45 sec. calc after it repeatedly failed in the real world
at
>any place between 70 sec and 80 seconds.  The contractor used it after the
>fact when they failed the 60 second test on at least 3 occasions.  Tyco did
>the calc's not the contractor, I checked the input.  This was not long
>after
>it was released.  




My mistake Chris....sorry to put words in your mouth. Was not my intent. 

Even since we have been using the software there have been several factors
identified by Tyco that would cause delay in the real world. Such as delay
in the start-up of fire pumps and large underground loops causing delay
because of inertia. 

Ken Holsopple
Designer
Rowe Sprinkler Systems, Inc.