There was a change in the 13 ROP that addresses this issue.  It points  
out that even when water delivery is calculated, the acceptance test  
still requires a timed delivery for future ITM.  It states that if a  
single outlet takes longer than 70 sec then it must be evaluated.  To  
be honest, there is now a need to better coordinate with the option of  
manually testing using more than one sprinkler.

Roland

On Jun 17, 2009, at 11:36 AM, Travis Mack wrote:

> I did a couple of preaction systems about 3 years ago.  The FDT and  
> field
> tests were within 1-2 secs if I recall correctly.  I was pretty  
> impressed.
> We did have a fire pump and tank on the project, so there would not  
> have
> been any variability from a city supply.
>
> The systems were large (+/-1200 gallon capacity) and that is why we  
> did
> the FDT to make sure it worked before installation.
>
> We did have the Tyco DV-5 preaction valve and the QRS accelerator on  
> the
> system.  The FDT would not work with our looped system.  We had to  
> make it
> a tree for the FDT to work.  Tyco says it works on simple loops,  
> which is
> what we had, but it would not work.  We sent the file to tech support.
> Their response was: Well, I guess it won't work on a loop like that
> either.  So, a minor bump in pipe size and all went well.
>
> FYI - The fire pump on the system was a 150 psi @ 1500 gpm diesel  
> pump.
>
>
> Travis Mack