Let me clarify, I thought it was way too far off in the 1 example I was
involved with.  45 sec. calc after it repeatedly failed in the real world at
any place between 70 sec and 80 seconds.  The contractor used it after the
fact when they failed the 60 second test on at least 3 occasions.  Tyco did
the calc's not the contractor, I checked the input.  This was not long after
it was released.  

I withhold final judgment until I hear more actually experience.  My first
impression was not good.    

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ken Holsopple
(forum)
Sent: Wednesday, June 17, 2009 2:26 PM
To: [email protected]
Subject: RE: Slow responding dry pipe valves-FDT

Mike Brown wrote:

>But what happens when then software shows the system tripping in the
>required amount of time...then when it comes time for final inspection
>with the AHJ and it doesn't work? That could be costly mistake !?

Mike,

Just went through some FDT training (refresher course) and have been using
the program for about three years. 

Keep in mind that the program carries a UL Listing. It has been tested in
comparison with "real world" application and as Chris and others stated it
is pretty close. The 2007 edition expanded and clarified on the testing
procedures with regards to using the software and testing the system. You
may want to take a look. The new edition of 25 also had some changes with
regards to freezer facilities and regular testing of dry systems that were
designed using the water delivery software.

The new acceptance test/inspection procedures provide guidance to what I
like to equate to a main drain test. Comparison to the previous years
results no matter if they are over 60 seconds or not. It also provides an
alternate method using a "manifold" with several outlets depending on the
hazard protected.

Like any other program.....garbage in means garbage out. You have to mind
your p's and q's, but I would not consider it any worse than running
hydraulic calculations. Just a couple of more variables like air pressure
and trip ratio for the valve, etc.

And yes, I can say for sure that any mistake I make carries a price tag. I
keep that in mind every time I input data and hit the calculate button.

Ken Holsopple
Designer
Rowe Sprinkler Systems, Inc.




_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to