See NFPA 13R 6.6.7.1.3 (2002 ed.) & 6.7.7.1.3 (2007 ed.)

BK

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Thursday, June 18, 2009 2:59 PM
To: [email protected]
Subject: RE: 13D Question 1988 Edition

In all my almost 40 years experience,I have never seen anything 13,13D, or
13R
limit the number of sprinklers in a compartment.There must be a
misinterpretation
on the part of the AHJ.It happens.

Lamar Vaughn,SET


---- "Travis Mack wrote: 
> Again, going from memory as well.  Isn't / Wasn't there something saying
> that you need to use the fewest number of sprinklers able to protect the
> area.  So, if you have a 20'x30' room, you need to use 2 sprinklers at
> 20'x20' spacing, instead of using 4 at 16'x16'.  Using 2 sprinklers, you
are
> calculating flowing 40 gallons for the 2 sprinklers vs 26 gallons for 2
> sprinklers  with 4 heads in the room, both scenarios protecting the same
> space.  Is that possibly what he is referring to?
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Bob Knight
> Sent: Thursday, June 18, 2009 12:36 PM
> To: [email protected]
> Subject: RE: 13D Question 1988 Edition
> 
> Mike,
> Going from memory, I don't have any standards with me, there is a
> requirement for QR sprinklers not exceeding 4.  I believe that this is
> actually a 13R requirement though.  Maybe this is the confussion.
> 
> Bob Knight
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Mike Cabral
> Sent: Thursday, June 18, 2009 12:06 PM
> To: [email protected]
> Subject: 13D Question 1988 Edition
> 
> I have an AHJ that is telling a designer that there can not be 4
sprinklers
> in a single compartment. I was told that he is working off an old standard
> from 1988 or so. Anyone have recollection of this. 
> 
> Mike Cabral
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> 
> 
> 
> 
> __________ NOD32 4168 (20090618) Information __________
> 
> This message was checked by NOD32 antivirus system.
> http://www.eset.com
> 
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to